Thank you. I got the first panel for free but, I do plan to add 3 more panels as 2 will get morning sun and 2 panels on the back get afternoon sun due to position of shed. My thoughts were to wire the front in series and the back in series, with the front and back wired in parallel. Would this be an issue? So it sounds like I need to be 12v. Is this correct?
If you plan to get the 24v battery, you will need to run the system at 24v for the SCC. Not sure which 20amp SCC you have, if you read the spec, I am sure it can do it. Make sure it can do 12v/24v. Could you list the SCC brand or spec to double check?
For example:
Two series(12v+12v=24v nominal) in the front ; assume 6amp
Two series (12v+12v=24v norminal) in the back; assume 6amp
Then parallel the front and back (24v +12amp) together to the SCC. Just be mindful of the total voltage or amperage of the SCC parameters to the battery.
For example of the Victron SmartSolar SCC specifications:
When the solar panel said 12v nominal voltage, the open circuit voltage could be 18v to 23v per panel(see below for the example solar panel spec)
The total of the two in series will be in the range of 36v to 46v.
Parallel the front and back, the voltage stays the same, the amperage increases. In this case, the assumed number will be 12amp.
The charge controller that will fit for the setup with 24v, the wattage (400W) and amp at 12amp would be the MPPT 75/15 or 100/15 or the 100/20.
Specification:
1pcs 100W monocrystalline solar panel(Grade A solar cell )
Model Type:SG-100WM Rate
Maximum Power:100W
Voltage: DC 12V
Output Tolerance:±3%
Voltage at Pmp:18.5V
Current at Pmp:5.41A
Open-Circuit Voltage:22.4V
Short-Circuit Current:5.9A
Maximum System Voltage:1000V