I would go to those forums and ask that question. I can't read the mind of every poster. Perhaps there are specific reasons that would apply to specific use cases? Perhaps they are off the grid or their equipment says to earth ground. Perhaps it depends on the voltage? It all depends on where you are standing. Do you understand the risks of earth grounding a 48 volt pack versus a 12 volt pack?Ive read some forums saying that the battery packs should be earth grounded, then some saying no or they dont earth ground their battery pack?
So they are saying, you can ground either side of the battery and make it work, but then you have to have the appropriate inverter chassis bonding, and you have to realize that the AC outputs are still isolated from that ground.If you ground the battery, you can ground it at the positive terminal or at the negative terminal with a grounding conductor. SMA Solar Technology AG does not recommend grounding the battery. If the battery is grounded, the enclosure of the Sunny Island must also be grounded. This additional grounding is no substitute for the grounding at connections AC1 und AC2.
The Midnite Classic has both Arc Fault and Ground Fault protection. You ground the Classic, and its internal GFP bonds it to negative. Does that answer your question?So, I did a little reading, and now I'm not sure if I understand the scope of what @SolarQueen said.
The codes are pretty clear that an arc fault/ground fault protection device is required for 'PV systems' on buildings. And by the definition of what a ground fault protection device has to do, its clear that a ground is required at the device. So I'm clear on all that.
However, I can't find anything applicable to the battery system. The NEC code Article 706, under Scope, says it applies only to DC battery systems over 60 volts. I'm not sure that the code requires ground fault protection at the battery, unless that is included as part of the 'PV System'. I looked for a definition of the 'PV System' and didn't see one, but the diagrams distinguish the 'PV System" from the 'ESS System'. So if a person was just running a Sunny Island as a grid powered battery backup with no photovoltaic system, does the ground fault requirement still apply?
I'm not sure if the Midnight Classic arc fault protection also detects faults down stream of the charge controller, or if it only detects them upstream. At any rate, it can't disconnect the battery from the inverter. I'm thinking that appropriate wire sizing relative to the battery over current protection is the actual protection between the battery and the inverter.
Anyway, I might be splitting hairs there with the exception that I need to figure out if my Midnight Classic charge controller also ties one of its DC outputs to ground because I need to account for that in the wiring of the Sunny Island. I'm sure that's in the Midnight Classic documentation.
In regards to the Midnite Classic it does. Thanks.The Midnite Classic has both Arc Fault and Ground Fault protection. You ground the Classic, and its internal GFP bonds it to negative. Does that answer your question?
And they define Utilization as basically "end use equipment"Photovoltaic (PV) System. The total components and subsys‐
tem that, in combination, convert solar energy into electric
energy for connection to a utilization load.
So by that I understand any requirements for the 'PV System' apply to the storage system and inverter, as they are conversion equipment, not utilization equipment.Utilization Equipment. Equipment that utilizes electric energy
for electronic, electromechanical, chemical, heating, lighting,
or similar purposes.
The only exception I see for the ground fault protection requirement in the 2014 code is:@SolarQueen, thank you for the spec sheet but my system is a stand alone system. But even with my system a GFP is still required aint it?
So if your solar power is generated on top of a building or is used in a building, you need the ground fault protection.Exception: Ground-mounted or pole-mounted PV arrays
with not more than two paralleled source circuits and with
all dc source and dc output circuits isolated from buildings
shall be permitted without ground fault protection.