EG6000EX vs 6000XP

Okay...here are the settings I'm using for my inverter:

Option 14 Battery Type EG4
Option 19 Low DC Cut off battery voltage setting (EG4) 20%
Option 20 Bypass loads to grid when grid is present (EG4) 30%
Option 21 Set point for transfer back to off-grid operation is bypassed based on option 20 (EG4) 95%
Option 30 Scheduled Start Charging time for AC charger Default is 00 (midnight)
Option 31 Scheduled Stop charging time for AC charger Default is 00 (midnight)
thank you so much. going to give it a try and let you know. Appreciate it!
 
Mlhagema, it looks like you are isolating the efficiency of the charge controller and missing the mppt efficiency issue I have highlighted. If your pv input measurement was before the 6000ex unit and the second reading is at the battery it would also show the pwr consumption of the 6000ex unit of around 115w.

If you have a clamp meter just take a voltage and amp measurement on the pv line before it connects to the 6000ex unit and compare that to pv input pwr of the watchpower readout. Or just compare it to the 6000ex readout. I think you will see around a 250w loss there and another 115w loss by the time it gets to the battery.
 
Okay...here are the settings I'm using for my inverter:

Option 14 Battery Type EG4
Option 19 Low DC Cut off battery voltage setting (EG4) 20%
Option 20 Bypass loads to grid when grid is present (EG4) 30%
Option 21 Set point for transfer back to off-grid operation is bypassed based on option 20 (EG4) 95%
Option 30 Scheduled Start Charging time for AC charger Default is 00 (midnight)
Option 31 Scheduled Stop charging time for AC charger Default is 00 (midnight)
I tried inputing your settings but options 19,20,21,30 and 31 would not allow a % setting. They showed voltage settings instead. I suppose I may need to update the firmware to use your settings...
 
I was running a TP6048 (6000ex close relative) for about a year.
I'd suggest you ditch communications with the inverter, set your battery to user and run everything off voltage.
14 - USE
17 - 55.2V or close to it.
18 - 54V or close to it. (54.8V should balance the cells if you don't get a full charge daily and they start to drift).
19 - 44V or higher
20 - 51V (this is the highest you can go and should keep you around 25% soc)
21 - 53V (this will keep your grid use to a minimum, you can bump it up if you have bad weather coming or want to charge fuller from the grid)

There is a thread on here somehow that has lots of different users settings, search for LVX6048 settings or something along those lines.

Note that I never updated the firmware on my TP6048, everything worked well enough out of the box.
I will give this a try
 
I tried inputing your settings but options 19,20,21,30 and 31 would not allow a % setting. They showed voltage settings instead. I suppose I may need to update the firmware to use your settings...
Is option 14 set to EG4? That switches the others to percentages.
 
I was running a TP6048 (6000ex close relative) for about a year.
I'd suggest you ditch communications with the inverter, set your battery to user and run everything off voltage.
14 - USE
17 - 55.2V or close to it.
18 - 54V or close to it. (54.8V should balance the cells if you don't get a full charge daily and they start to drift).
19 - 44V or higher
20 - 51V (this is the highest you can go and should keep you around 25% soc)
21 - 53V (this will keep your grid use to a minimum, you can bump it up if you have bad weather coming or want to charge fuller from the grid)

There is a thread on here somehow that has lots of different users settings, search for LVX6048 settings or something along those lines.

Note that I never updated the firmware on my TP6048, everything worked well enough out of the box.
I would be curious to know if someone could help me with similar settings on a 6500ex. I have it now using battery communication and it will charge from the grid at 20% and stop at 25%. I would switch over to user settings but not sure how to get the same results with those settings.
Thanks
 
I would be curious to know if someone could help me with similar settings on a 6500ex. I have it now using battery communication and it will charge from the grid at 20% and stop at 25%. I would switch over to user settings but not sure how to get the same results with those settings.
Thanks
Can you post what settings your 6500ex has?
 
Last edited:
unfortunately I don't even have a computer hooked up to it. It looks like I need to dig in and tackle that side of it
Just looking at the manual. Seems like there’s something wrong.
 

Attachments

  • IMG_0855.jpeg
    IMG_0855.jpeg
    235.3 KB · Views: 24
  • IMG_0856.jpeg
    IMG_0856.jpeg
    248.9 KB · Views: 23
Last edited:
Can you post what settings your 6500ex has?
I will try to get those tomorrow. Thanks

Long delay - sorry been away
#
Value
Description
01
Sbu​
Output Source Priority​
02
120​
Max charging current​
03
APL​
AC input voltage range 80-140​
05
EG4​
Battery Type​
06
Lhd​
Overload Auto Restart​
07
Ehd​
Temp Auto Restart​
09
60​
Output Frequency​
10
120​
Output Voltage​
11
10​
Max Utility Charging​
12
20​
SOC > Utility SBU​
13
25​
SOC > Battery SBU​
16
SNU​
Charger Source Priority​
18
bOF​
Alarm Control (off)​
19
HEP​
Display Auto Return (off)​
20
LON​
Backlight Control (off)​
22
AON​
Beep Alarm (off)​
23
Byd​
Overload bypass (enable)​
25
Fs5​
Record Fault Code (disable)​
26
56​
Bulk Charge​
27
56​
Float Charge​
28
SIG​
AC output mode​
29
10​
Low DC Cutoff​
30
Ed5​
Battery Eq​
31
58.4​
Battery Eq Volt​
33
60​
Battery Eq Time​
34
120​
Battery Eq Timeout​
35
30d​
Eq Interval​
36
Ad5​
Eq activated Immed​
37
NHE​
Reset Stored Data​
41
dd5​
Max discharge current​
51
LEN​
On/Off RGB LED​
52
NOH​
LED Brightness​
53
LON​
LED Speed​
54
Bfe​
LED Effects​
55
C02​
LED Color​
 
Last edited:
the settings Sig Solar tech had me input:

14 use
17 56.0v
18 56.0v
19 45.0v
20 46v
21 54v
22 I-EP
23 LON

I tried setting 14 to EG4 and then letting the menu return to see if the following inputs would turn to percentages but they did not
 
the settings Sig Solar tech had me input:

14 use
17 56.0v
18 56.0v
19 45.0v
20 46v
21 54v
22 I-EP
23 LON

I tried setting 14 to EG4 and then letting the menu return to see if the following inputs would turn to percentages but they did not
You need to apply the change for it to work. You can't just let it return to the menu following a timeout.
 
You need to apply the change for it to work. You can't just let it return to the menu following a timeout.
I understand. I did that and the other values did not turn to percentages, they remained voltage values. Probably a glitch in the original firmware.

That is, unless I misunderstood how to apply the change. I pressed the menu button for 3 seconds to enter the setting menu, selected 14 and changed to EG4, then I pressed the menu button again to apply the change.
 
Last edited:
I understand. I did that and the other values did not turn to percentages, they remained voltage values. Probably a glitch in the original firmware.

That is, unless I misunderstood how to apply the change. I pressed the menu button for 3 seconds to enter the setting menu, selected 14 and changed to EG4, then I pressed the menu button again to apply the change.
If you didn't press Enter one last time after changing the setting, then it's not applied...
 