    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    Thank you so much for help and guidance with such details. I have learnt a lot from this forum.
  2. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    I have another question, most of the the day I don’t have load shedding and battery is full at 100%, I read keeping lithium artery at 100% is not recommended, so how can I limit the full charge at 90%
  3. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    I have made the changes. Float 51.5 Absorption 52.5 Equalisation 52.5
  4. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    After a day of being fully charged its voltage a came down a little. It’s now at 50.79
  5. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    Here are the current setting as per your recommendation. Thank you. The installer set the equalization days to 90. I have now changed it to 0. I need help with setting the correct ‘ Micro Inv input’ values What it does is to allow battery to be used by ACs from ON volts till OFF volts and...
  6. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    There is no option to disable equalisation. So should I set the following Float v 51.5 Absorption V 51.7 Equalisation 51.5 Please advise
  7. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    Would you suggest that I enable the float charge ?
  8. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    So I am going to check “Disable Float Charge” The battery is not connected to a BMS port on inverter and installer said it has one built in. Here is the picture of full setup and battery.
  9. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    I have made the following changes. Thank you so much for such details and help. Also there is a setting which the installer said that I need to adjust as per my requirements to use the battery for ACs. It’s as Micro INV input values. Which I want to use so when there is no grid or solar I can...
  10. X

    Float, Absorption and Equalization V for Lithium Battery ESM-48100B1

    Hello, I recently got a 8KW Hybrid Solar System installed at my home. The company who installed the system have set the setting, which I am not sure if they are correct. I am using 580w x 18 Jinko Bifacial Panles, with 8KW Inverex Nitrox Hybrid Inverter and a Lithium Battery ESM-48100B1. I have...