    Seeking help with Growatt/BigBattery settings

    Hello, I don't know the answer to your question, but would you mind sharing which Growatt inverter you have? Is it the 6000TL-X? Was it pretty simple to set everything up? I'm looking at a battery pack + inverter, but no solar, no batteries, no scheduling, etc. -- literally just the battery...
  2. A

    Simple, reliable 120v or 240v inverter than can output ~3000W from a battery bank? No solar; no generator; no scheduling.

    Thanks for the response. Was it reasonably easy to set up? Given how simple my needs are (no scheduling, no solar, no generator, etc.) I hoping to find something that doesn't require me to be an expert and go through 1000 menu settings just to get it operating in the simple manner that I need...
  3. A

    Simple, reliable 120v or 240v inverter than can output ~3000W from a battery bank? No solar; no generator; no scheduling.

    I'm thinking about a very simple setup. A 120v Reliance Controls manual transfer switch that is powered by a battery system + inverter when in "GEN" mode. 10-15 kW of battery capacity, probably EG4. All I need the inverter to do is keep the batteries charged and to output (up to ~3000W) to...
  4. A

    Is AFCI+GFCI breaker tripping in main panel inevitable when using a Reliance Controls Manual Transfer Switch?

    Thanks for the input. My plan was to do the same thing -- leave the circuits on GEN all the time. So when exactly is it that you get the trips? Only when you are switching between LINE and GEN? Also, I haven't seen much discussion of the Reliance Controls Neutral Kit...
  5. A

    Is AFCI+GFCI breaker tripping in main panel inevitable when using a Reliance Controls Manual Transfer Switch?

    Thanks for the input. I think your paragraph about "immediate A/B transfer between two non-synchronized AC sources" is may be the part that would be relevant to my concern. Would that apply if you are outputting from the inverter to a transfer switch using pass-through mode from the grid, and...
  6. A

    Is AFCI+GFCI breaker tripping in main panel inevitable when using a Reliance Controls Manual Transfer Switch?

    I've read a bit about people getting C/AFCI+GFCI breaker trips in their main panel when they are using a Reliance Controls manual transfer switch (MTS). I understand that this has something to do with neutral switching and/or neutral+ground bonding issues. Apparently the main panel breakers...
  7. A

    EcoFlow Delta Pro and transfer switch setup

    Quick question about the nuisance trip on c/afci + gfci circuits when switching from LINE to GEN. Does that happen b/c of something going on in the Delta Pro? Does the Delta Pro inverter bond neutral & ground? I'm thinking about doing a similar setup with a Reliance transfer switch, but...
  8. A

    Is there a "most recommended" battery brand for value/safety/reliability?

    I see Fortress, HomeGrid, Signature Solar, and BigBattery getting mentioned a fair bit on this forum and other forums. For larger capacities in the 15-25 kWh range, it looks like Fortress and HomeGrid are up in the range of $500-600 per kWh for just the battery and seem to have decent to good...
  9. A

    Question about Sol-Ark 15K with 200amp pass-through -- suppose an EV charger is running when the grid goes down...

    Could you provide a link to the type of smart switch you are talking about? My EV charger is really the only load that I would need to shed.
  10. A

    Question about Sol-Ark 15K with 200amp pass-through -- suppose an EV charger is running when the grid goes down...

    Can you tell me more about that? Is that a setting within the Sol-Ark that allows you to do that? Or separate equipment?
  11. A

    Question about Sol-Ark 15K with 200amp pass-through -- suppose an EV charger is running when the grid goes down...

    Thanks for the response. I guess some load shedding setup might work. I was mostly just seeking confirmation that if you're doing 200amp pass-through to your main panel, the default behavior of the inverter would be that batteries would take over for EVERYTHING in the main panel during a grid...
  12. A

    Question about Sol-Ark 15K with 200amp pass-through -- suppose an EV charger is running when the grid goes down...

    Say you have a Sol-Ark 15K doing 200amp pass-through from the grid to your 200amp main panel. Say you've got a battery backup system hooked up to it. And say you are charging your EV at, e.g., 7.2 kW. Because the 15K is doing pass-through to the entire panel rather than to a critical loads...
  13. A

    EcoFlow Delta Pro / Transfer switch/ AC Charging

    I'd been thinking about buying a Delta Pro and Smart Home Panel but decided against it b/c its not really compatible with a large (11-12 kW) professionally installed solar array that I'd like to have installed in a year or two. Did lack of compatibility with large solar arrays dissuade you at...
  14. A

    Best options for getting battery backup ASAP (probably DIY) while planning on solar panels professionally installed in 1-2 years

    Hah hah, I think it's just doing a generic Google maps search for "PNW" when you click on that, so it brings up whatever is near you.
  15. A

    Best options for getting battery backup ASAP (probably DIY) while planning on solar panels professionally installed in 1-2 years

    I'm in the US. PNW listed next to my name refers to Pacific Northwest. Hah... maybe I should be more specific.
  16. A

    Best options for getting battery backup ASAP (probably DIY) while planning on solar panels professionally installed in 1-2 years

    This thought had crossed my mind and I was also planning on calling around. That's pretty frustrating. What did you end up doing?
  17. A

    Best options for getting battery backup ASAP (probably DIY) while planning on solar panels professionally installed in 1-2 years

    Very helpful. Thank you! One quick follow up question: When there's a grid outage and your off-grid inverter switches from pass-through mode to battery mode, how fast is the changeover? And is the changeover speed dictated solely by the inverter? Or does the manual transfer switch have some...
  18. A

    Best options for getting battery backup ASAP (probably DIY) while planning on solar panels professionally installed in 1-2 years

    Thanks for the response. I read your linked post about common neutrals and, to be honest, most of it was a bit above my head. As to option (3), if I purchase one of the higher end inverters with the neutrals that are permanently wired together internally, is there any danger or NEC violation...
  19. A

    Help with home battery backup system

    Can you tell me more about this setup? I just posted a new post on this forum, and your setup sounds like my option #3: https://diysolarforum.com/threads/best-options-for-getting-battery-backup-asap-probably-diy-while-planning-on-solar-panels-professionally-installed-in-1-2-years.53309/ Is it...
  20. A

    Best options for getting battery backup ASAP (probably DIY) while planning on solar panels professionally installed in 1-2 years

    Increasingly frequent power outages have led me to decide that I need a backup power solution ASAP even though I won't be able to have solar panels installed for another year or two. I'd like to choose batteries + inverter now that will be usable with a future 11-12 kW professionally installed...