    Dreaded 61 issue SG TP6048 with 2 Sungold 48100m

    User mode is not an acceptable longer term answer I bought all Sungold branded system to avoid problems like this and have something that works with an advanced BMS to ensure longevity of the cells improve charging efficiency etc. and that is not turning out to be the case.
  2. B

    Dreaded 61 issue SG TP6048 with 2 Sungold 48100m

    1, set battery type as pyl in the inverter 2, set on the battery screen 485 protocol as XY39 3, set ADD on the battery as 1 0 0 0, 4,use the communication cable go with the inverter, the side had INT label goes to inverter 485 LioN port, the side with BAT label goes to 485A port. Resolved the...
  3. B

    Dreaded 61 issue SG TP6048 with 2 Sungold 48100m

    I am having a problem with getting the BMS working and it is frustrating as heck. The cable from Sungold is even labeled INV on one end and BAT on the other all contacts work and I even double checked the pinout with an ethernet tester. Even still I tried reversing it just in case it was...
  4. B

    Lv6548 firmware updated, still error 61

    Not to be picky but why in the world would they pin out differently and not just design the system to use a standard ethernet cable?
  5. B

    Newbie hello and probably a dumb question net meeting

    Hello, I recently put together a off grid backup system consisting of a Sungold power 6048 240v all in one inverter and 2 x Sungold 5.12 KW 48v batteries and 10 X 545w Panels installed on my roof. I do not have net metering meter installed, but turn "Solar feed to grid" on my solar inverter will...