For 12 and 24 volt systems Blue Sea range are highquality,can suggest me on Amazon
For 12 and 24 volt systems Blue Sea range are highquality,
Thanks, why then are these switches made with the positive in common? As you wrote, then a disconnector with positive and negative as in the photo is better.For a selector switch you would need one that can switch both positive and negative at the same time. You do not want to leave the negative from both packs connected all the time.
Mike if the English translation is correct you are saying to put AGM and Lifepo4 together or rather in parallel??For 12 and 24 volt systems Blue Sea range are highquality,
Further investigation suggests you have a 48 volt system so the above are not rated for that.
I may have discussed the concept of having two different battery packs before. You could just connect the AGM and lithium together and charge/discharge in parallel. Use a charge voltage for lithium, 56.8 volts.
When running loads, your inverter, the lithiun will carry out most of the work until around 30% SOC when the AGM will add power.
It's possible the lithium pack alone will be enough for your needs and retire the AGM.
OK I understand, switching between packs may require inverter pre charge circuit if there is complete disconnection, and possible implications with the solar controller. As I discussed above a very simple option is to parallel the two packs.He is switching between two banks of 48v batteries
I was saying , you have a 48 volt lithium pack and a 48 volt AGM pack. Two 48 volt batteries. Connect these in parallel and charge with lithium settings. ( need suitable fuse on each pack pack for safety).English translation is correct you are saying to put AGM and Lifepo4 together or rather in parallel??
Mike, there are some users who have done it, but other 'expert' users said it is inadvisable for security reasons to do so. The reason seems to be linked to the fact that if, for example, one of the AGM series batteries (12Vx4) shorts out, the lithium batteries immediately deliver all their power to the AGM batteries, causing dangerous overheating. Furthermore, I believe that even if the charging voltages for the lithium I bought are similar, the charge could be unbalanced.OK I understand, switching between packs may require inverter pre charge circuit if there is complete disconnection, and possible implications with the solar controller. As I discussed above a very simple option is to parallel the two packs.
It's probable the AGM batteries are well past their best, they are not deep cycle heavy duty batteries, and it may be better to take them out of the system, and allow more efficient use of the available solar to charge the lithium and power loads .
Mike you say to put in series between a positive for the agm and the positive of the life example 2 ANL of 100 amps?I was saying , you have a 48 volt lithium pack and a 48 volt AGM pack. Two 48 volt batteries. Connect these in parallel and charge with lithium settings. ( need suitable fuse on each pack pack for safety).
I an also adding the suggestion that you may not need the AGM to power your loads. There may be enough storage in the lithium pack.
Yes , fuse each pack. The idea of having the two packs in parallel, Is not ideal, but a method that some use.Mike you say to put in series between a positive for the agm and the positive of the life example 2 ANL of 100 amps?
Mike, no I really don't need it, but I would like to use it as a backup. In the sense that if the lifepo4 batteries are a little flat and I need more energy I can use the agm ones. They are now about a year and a half old, and they work reasonably well.Yes , fuse each pack. The idea of having the two packs in parallel, Is not ideal, but a method that some use.
A further point I am making is, do you need the AGM pack ?
Will the lithium alone power your loads?
Hi Mike, this would be the sketch of what I would like to do with both batteries, unfortunately carrying out the procedure of turning off the inverter in case of need for energy. What do you think?Yes , fuse each pack. The idea of having the two packs in parallel, Is not ideal, but a method that some use.
A further point I am making is, do you need the AGM pack ?
Will the lithium alone power your loads?