When working with the 6000XP and the minimum 200Ah battery bank recommendation is met with all paralleled inverters, it's important to set the appropriate discharge current limit, especially when multiple inverters are paralleled.
For example, if you have two 6000XPs in parallel with 600Ah worth of batteries in the battery bank, you will want to set the discharge current limit to 280A.
Properly configuring the discharge current limit helps prevent common issues in paralleled systems, such as EPS overload or unexpected switching to grid bypass even when the battery percentage is above the on-grid discharge threshold. By ensuring the discharge settings are aligned with your setup, you can maintain smooth operation and avoid these troubleshooting headaches.
For optimal performance, always refer to your spec sheet and make necessary adjustments to the discharge current limit based on the number of paralleled inverters. This proactive approach ensures reliable and efficient energy management in your system.
For example, if you have two 6000XPs in parallel with 600Ah worth of batteries in the battery bank, you will want to set the discharge current limit to 280A.
Properly configuring the discharge current limit helps prevent common issues in paralleled systems, such as EPS overload or unexpected switching to grid bypass even when the battery percentage is above the on-grid discharge threshold. By ensuring the discharge settings are aligned with your setup, you can maintain smooth operation and avoid these troubleshooting headaches.
For optimal performance, always refer to your spec sheet and make necessary adjustments to the discharge current limit based on the number of paralleled inverters. This proactive approach ensures reliable and efficient energy management in your system.
Last edited: