I currently have the EG4-6000EX and it is a terrible unit for off-grid use. Everyone knows about the high idle consumption (115w) but there also looks to be a 250W loss from the PV input to the PV output (MPPT loss/pwr consumption). The 250w looks to be consistent across the full pwr input range but is a killer at low pv input (overcast days). Assuming 20% panel efficiency when poor conditions you have to get over the 365w hurdle before you can supply to the load or start charging your battery(s). 365w / 20% = 1.825kW of added pv array to manage bad days so saving $ on this inefficient inverter cost you $ on additional panels.
I was running a Schneider SW4048 for 6 years with no issue on bad days. After I switched the unit out to this 6000EX I had to increase my pv array to manage poor days. $0.70 per watt installed (conservative) x 1.825kW = $1,278 to get back to where I was before the changeout. Here are some of the measurements taken showing the loss between the measured pv input (+ wire at the inverter) against the pv output reading on the display of the 6000EX unit:
![pv table.png pv table.png](https://diysolarforum.com/data/attachments/174/174269-65d33347842758140d1494e1ab74fc17.jpg)
I have 2 questions.
1/ Has anyone on this forum verified this mppt loss/pwr conumption of around 250w?
2/ The new 6000XP unit has much better idle consumption but has anyone measured the mppt loss/pwr consumption?
Will, love to see you test this mppt efficiency with low pv input. 95%+ mppt efficiency is great at high pv input (sunny day) but for off-grid what really matters is the bad days and efficiency on the low pv input days is what is really important.
Side note - SS has terrible customer service. Very difficult to connect with, techs only know product spec's and never acknowledge the issue raised. As we can see, they quickly discontinued the 6000EX and released this new 6000XP that again looks great on paper but?
Bruce,
I was running a Schneider SW4048 for 6 years with no issue on bad days. After I switched the unit out to this 6000EX I had to increase my pv array to manage poor days. $0.70 per watt installed (conservative) x 1.825kW = $1,278 to get back to where I was before the changeout. Here are some of the measurements taken showing the loss between the measured pv input (+ wire at the inverter) against the pv output reading on the display of the 6000EX unit:
![pv table.png pv table.png](https://diysolarforum.com/data/attachments/174/174269-65d33347842758140d1494e1ab74fc17.jpg)
I have 2 questions.
1/ Has anyone on this forum verified this mppt loss/pwr conumption of around 250w?
2/ The new 6000XP unit has much better idle consumption but has anyone measured the mppt loss/pwr consumption?
Will, love to see you test this mppt efficiency with low pv input. 95%+ mppt efficiency is great at high pv input (sunny day) but for off-grid what really matters is the bad days and efficiency on the low pv input days is what is really important.
Side note - SS has terrible customer service. Very difficult to connect with, techs only know product spec's and never acknowledge the issue raised. As we can see, they quickly discontinued the 6000EX and released this new 6000XP that again looks great on paper but?
Bruce,