Hey Everyone, looking for some direction and help!
So this is an off grid system with no solar panels at the moment - a 22kw and a 37kw generator are available
One of the generators will be used to charge the following battery bank
There are 5 - 48v Battery Banks
Each Bank is made up of 24 - 2V - 152Ah @ 8HR to 1.75V
Absolyte GP - 50G07
Here is the battery Manual
Here is the constant current charts
These battery banks will be connected to 2 - SOL-ARK12s in parallel
I understand my battery banks will have a capacity of 760AH @ 48V
I’m having trouble determining settings for Max Amps charging and discharging in the SOL Ark
attached is a picture from battery specs where it says the max charge current is 5% of C100 Rating and the chart looks to show it as 210 - 5% being 10.5A
Any help greatly appreciated!
Thanks!