EG4 18K - Air Conditioning won’t run without grid

EG4 PowerPro battery, 14.3kW 280Ah, 200A max discharge, 306lbs !!!! x2 should be plenty

It's the surge LRA that is the problem, I don't think there is enough battery to handle the surge. PV can help but with a large surge it has losses.

I don't believe in running things to the max, it is hard on equipment. That in itself would make me install a pair of 18Kpv's and probably 4 batteries.

Any other loads on the system with a grid down situation and the 18Kpv with the 2 Power Pro's won't probably work.

Reading this article, one could use 2.5 x 5000W running and see surge at 15Kw. https://eepower.com/technical-artic...rical-load-for-stand-alone-pv-system-sizing/#

I don't know where or how you got to this
There are conversion losses also and that affects output.
 
Do you have all 4 battery terminals on the 18Kpv occupied with Battery cable? If not, this could starve the 18Kpv.
 
You should get a MicroAir Easy Start. It makes a huge difference. I'm with Zwy, I think it's the batteries falling over with the surge. A normal 4T A/C can pull as much as 28000 watts during startup, meaning your battery has to produce 500+ amps for a moment... If your battery voltage drops too low it's going to cause resets.

I'm running a pair of 18KPV's with 60KWH of batteries. It always started my 4T, when I only had 30KW of battery (600A) but it seriously caused light flickering, UPS clicking, etc. It actually flicks the lights slightly when on grid if you are paying attention.

With the "Magic Start" the UPS's stopped clicking, and I don't really notice most of the time even in the hottest part of the summer on battery. It will likely let you get away with not buying more battery. In the summer peak my 4T can pull just under 5KW continuous (4.87). In milder cimates you will probably get away with something less.
 
Needs to be micro air 368-72

I tried the one SS sells and it wouldn't start when I was getting higher start amps.

I'm usually around 33 amps now with 4t. They also changed my firmware. I was on 1717 before what I have now. I also have no grid input at all
 
Copied from another thread.

So, we were having the same issue. I noticed the yellow arrows were feeding power to the EPS rather than standard consumption. I'm not sure what the EPS stands for but by reading what I did it was meant to be hooked up to a critical loads aka backup panel. Following the flow charts in the manual gets it set up this way.

What we did to fix it was turn OFF off grid mode. This moved the arrows to consumption mode rather than EPS. I don't know why EG4 labeled it the way it did, but EPS mode does not like very high inrush current. By switching this, we went from an 18kpv that wouldn't even start a 2 ton ac to one that would not only start the two ton, but start a 4 ton on an easy start with the 2 ton running and about 2k worth of normal loads.

I'm not sure how it'll work without grid connection but I would think it would do the same.

In brief, if your 18kpv won't start ac even with micro air soft start, turn OFF off grid mode.
 
While he did not say what brand, he did say he has a soft start.
A normal "soft-start" is an extra capacitor that is connected to the motor to provide more current to the start winding in the motor during the initial start, that is removed once the unit starts to keep from burning up the winding. Staring current is only reduced nominally. MicroAir actually limits current flow.

I did the same thing with a thermistor, actually worked pretty well, but during the summer would not stay off long enough to cool down. I was going to build something with a thermistor and a bypass contactor on a delay, but for $300-odd the MicroAir just seems to work. Their tech support was great as well.
 
A normal "soft-start" is an extra capacitor that is connected to the motor to provide more current to the start winding in the motor during the initial start,

You are referring to a hard-start. The OPe'r can clarify, but I'm pretty sure he has a soft start based on his LRA measurements after installing it.
 