Hello, I would be really grateful for experienced persons thoughts / input as I'm trying to avoid a mistake....
I have a 2S4P system that I am installing.
8 identical Panels, each panel: 330W, 32.6V (VMP), 10.2A (IMP) 10.9 (ISC)
My array is East / West, as a result I am over-panelling.
My...
I'm nearly there... advice please:
My system:
2S4P, each string has 2 x 330w panels, each panel output is: 32.6v (VMP), 10.2 (IMP), & 10.9 (ISC). this gives a max output of 2640w to the charge controller.
QUESTION:
1: Do I HAVE to use a combiner box, or could I use the standard mc4 connectors...
Hello,
( Heads up, I'm a newbie)
I am installing a solar array:
3s2p , 3 series 2 parallel
330w each panel
10.2A each panel
VOC 39.12v each panel.
Each series of 3 panels combined output is: 117v and 10.2A ( with a total array output therefore of: 117v and 20.4A, 1980W)
I have the Victron...
Hello,
I've just mounted my solar panels and I'd very much appreciate someone to spend a couple of minutes to check if my results are to be expected.....
Here's the spec:
Solar self build Generator Spec:
300Ah LifeP04 battery, max continuous charge rate 150A <
150v/70-Tr Victron SmartSolar...
Hello,
I am about to mount a further 2 panels to my small emergency system, and I would very much appreciate if an experienced person here ( not a newbie like me- thanks) would take a quick look and comment if it's wrong! ( or right ? :) )
Please take a look at my numbers / panel configuration...
Hello,
Can I ask for advice please?
I have a heating issue that I do not understand, My positive lead to the inverter is going above > 50deg c. (and would go higher if left)
I have 1 x 300Amp battery, with a 12v1200 watt Victron inverter.
When the inverter is near load max output at 1130...