There is a new firmware released for the EG4 8k inverter, the firmware will be released on the EG4 website soon for download but I have linked it below as well as the updated manual. The ZIP file contains the new firmware, software, and a change log. If you have any questions or concerns please...
The EG4 3000 EHV-48 has a minimum PV input voltage of 120VDC. If your Solar array does not meet this minimum requirement then it would not be an acceptable input for this inverter unfortunately.
Hello Schinzul, With the EG4 Lifepower4 48v batteries you can close loop communicate with a maximum of 15 batteries (I have attached a diagram of the different DIP switch configurations). If you would like to add more 48v Lifepower4s to your bank you can add the EG4 communication hub to your...
Yes, the EG4 18kpv can be used with batteries that have no communication. On the inverter you would set the battery type to Lead-Acid and manually input the batteries charging/discharging parameters.
Hello dspecgsx,
Were there any changes at all done to the system when this issue started happening? Could you tell me when you updated to the latest firmware?
3.30 is the latest firmware and should be used if setting up closed-loop communications with Schneider. I have attached the updated parameters for 3.30 here.
There was an issue with the firmware on the eg4 website, it had a space in the file path causing an error. This has since been updated, could you redownload the firmware or erase any spaces in the file path when trying to update? If youre still experiencing issues other than this can you please...
You can enable Offgrid Output and Run Without Grid to achieve an off grid system, for the PV input selectors and quick charge not working if you would like to PM me your dongles information I can take a look at this for you.
Hello, I would like to assist you if you could provide me with some information. Are you using your generator as an AC input on both inverters? What are your generators specs? Could you tell me what your setting 42 is set to on both inverters? Thank you.
The firmware .zip was changed yesterday 11/13/23 4:05pm CST, if you downloaded it prior to then or from a different source than https://eg4electronics.com/backend/wp-content/uploads/2023/02/EG4-8K-Firmware.zip please re-download the .zip and see if you're encountering the same issue. Performing...
Hello, The EG4 LifePower4 batteries may need to be updated to the latest firmware to allow communication with Luxpower. The 48v firmware and guide can be located on the EG4electronics download page. https://eg4electronics.com/downloads/ If you're still having issues with this even after updating...
Can you move the unzipped firmware folder containing the .out and .axf files to your C: drive (C:\EG4-8k-firmware) and see if you're still getting this error?
Hello datuttlejr,
It sounds like you either have a bad BMS or something got disconnected on the BMS. If you're comfortable could you isolate the battery (confirm once again there is no voltage at the terminals with the breaker in the on position) then remove the top cover? Even though there may...
I was not able to get a definitive answer when trying to figure out if your generator is neutral ground bonded. If it is and your inverters setting 42 is set to dis then you potentially have 2 bonds in the system. Something to try next time you use your generator as an AC input is either turning...
@scottch Yes this inverter is designed to have AC input as well as PV input, if your PV is not capable of powering all of your loads the grid would assist in powering the rest.
Hello dcg9381, I have attached the latest manual (there are still changes being made to this but it does have setting 42 in it) as well as the latest firmware for the 6.5k. If you have any questions please let me know and I will be happy to help.