  • Post in thread: Random power outage EG4 6500 split phase

    Hello yall, not sure If this will help since I have EG4 6000EX, but I was having a similar issue at all different times, battery, solar. I am completely off grid and my power would go out for 3 to 5sec and come back on, been in contact with SS and as of yesterday EG4 had a new firmware update...
  • Post in thread: EG4 6000ex bonding question

    Here is a New video in reference to NGB.
  • Post in thread: Random power outage EG4 6500 split phase

    Well thought the issue had been resolved, I just had a power outage for about 5sec, batteries are @82%. Monday it went out 4 times in 1 hour. Made it 28 hours without an outage. I will continue to deal with SS, will post a update as soon as I hear back.
  • Post in thread: Is Solar Assistant-Raspberry PI a reliable remote monitoring/control solution

    This week I just hooked up the batteries directly to S.A. and I love it. I have EG4 LL ver1. It was a little bit of work due to the dip switches being inverse (off is on, on is off) once I got the correct addresses it worked. Just waiting on extra rj45 splitter for my 4th battery. I like that it...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Happy New Year everyone, may next year be productive and prosperous.
  • Post in thread: Ground fault from PV conductors Positive or Negative

    Thank you for the info, Solar Guppy mentioned that with non isolated inverters it will cause voltage potential on the conductors for the PV arrays. So I will try and gather more information on this issue. Thanks so much foe tour time.
  • Post in thread: Random power outage EG4 6500 split phase

    Negative they had me do 2 updates one last week for the "61" error and the one Wednesday which they claim it for the exact issues I'm having which is power outage for 3 to 5 sec and also switching for 120v to 110v volt after the shut down , however it does not change to 110v every time honestly...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Yea this issue is 1 of 3 that I have, I also have a problem with power outage for 3 to 5 seconds. It happened 4 times last night with no faults or errors, my system is also switching from120v to 110v during one of those outages. I'm also dealing with them in reference to this issue.Very...
  • Post in thread: Random power outage EG4 6500 split phase

    It's been an everyday battle with these units today while I was at work, and the sun was strong, I looked at solar assistant and it was showing like 1500 watts of solar I know that couldn't be possible due to the amount of sun. Usually I would be at about 98% by the time I get home and it was at...
  • Post in thread: Random power outage EG4 6500 split phase

    My system, Two EG4 6000EX in parallel, 4 EG4 LL VER.1, set on USE, I monitor batteries via SA, and only have 1 NG bond that I know of, Filterguy had me test for NG bond about a month back and the consensus was the the units I had didn't have a NG bond, however I got new units last month and have...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Here a new update from EG4 about NGB
  • Post in thread: Is Solar Assistant-Raspberry PI a reliable remote monitoring/control solution

    I ordered this one from Amazon and connected it to my battery buss. It works flawlessly, no adjustments needed.
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    @FilterGuy When I did the test yesterday, I had to remove the NG bond on my panel(this panel is where I have both inverters output going prior to the main panel) while I was reinstalling the bond I noticed real light sparks as I was tightening the ground screw. As such I checked with my meter...
  • Post in thread: Ground fault from PV conductors Positive or Negative

    Yes definitely, all of the testing and troubleshooting I have done has been dry. I only notice this some time in the middle of summer I actually have not tested during rain yet. As for water intrusion I'm not sure if that is or was the root cause, this might have been happening since I installed...
  • Post in thread: Random power outage EG4 6500 split phase

    Yes they all are frame grounded, also if you disconnect the panels from the system, the potential goes away, at the panel as well ad at the inverters.
  • Post in thread: Ground fault from PV conductors Positive or Negative

    I have checked at the breaker(have not actually pulled conductors from the inverters) as you seen in the picture showing 194+ voltage at the top of the breaker where it goes to the inverters as well as the bottom coming from the pv arrays, however I don't get that high voltage it's about 4 to 9...
  • Post in thread: Random power outage EG4 6500 split phase

    These inverters have a loud humming vibration type sound trying to attach file but it says type of file not allowed, what kind of file extension does it have to be?
  • Post in thread: EG4 6500EX Generator input

    Well the gen a have now is not inverter, its a reg 10000/8000, I'm debating whether or not to get the duromax 9000/7500 inverter ATS ready and parallel capability of course its $2000 And just sell my unit, or do what you have. How are you connecting to the batteries? Just direct to the buss bar...
  • Post in thread: EG4 6500EX Generator input

    Awesome, do you know the amp draw of those chargers? I just hate the money I spent on the panel and outdoor recptical for the gen. I gues I have a decision to make.
  • Post in thread: Random power outage EG4 6500 split phase

    This is crazy I had 3 more outages within the hour last night. Waiting on reply for SS.
  • Post in thread: Random power outage EG4 6500 split phase

    Hello Forum, I have an update. I got my replacement inverters and installed them on Saturday last weekend, I was very pleased on how I worked for 3 days, but on Tuesday early morning I had power outage again 3 to 5 seconds. Then two more days and it happened again, now it's happening every day...
  • Post in thread: Random power outage EG4 6500 split phase

    I'm really surprised that you have that low of potential on the positive. Mine has a lot more that that, It changes with the amount of irradiance coming in. In my original setup(Growatt), I found this potential by accident, I felt It tingle when I was washing my panels, and started...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Hello filterguy, thank you for yhe response, ok all potential off I have Meg ohms on output groud to neutral, Meg ohms input to output neutral and approx 24 volt neutral to ground with inverters on output line breaker off and generator input line on. I did get a reply from SS and this is what...
  • Post in thread: Random power outage EG4 6500 split phase

    I Checked and for some reason with 1.5k (its was a rainy day) off solar coming in to the inverters I still wasn't charging, I had to shut down and restart the system, it started charging after I did that.
  • Post in thread: EG4 6500EX Generator input

    Ok so that's 45amp draw on the gen, what size gen do you have?, mine is rated at 33amps, 10000/8000.
  • Post in thread: Random power outage EG4 6500 split phase

    Negative, everything had been the same had not done any changes. Friday was very sunny and it didn't charge by the time I got home its was dark so couldn't check it, yesterday it was showing about 340 volts, but like I said it was cloudy day the highest I seen yesterday was 2.4k from solar, I...
  • Post in thread: Ground fault from PV conductors Positive or Negative

    Hello Forum, I have a very odd issue. With a multimeter with one lead on positive or negative the other lead on ground(earth) I show voltage. The voltage varies depending on solar irradiance (in excess of 160v +). I have also used a oscilloscope to see the wave form and it has a very odd wave...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Ok I removed the NG bond in the panel output off at panel, inverters on battery/very little solar(its raining) and voltage is 31+ as shown on picture, when I reinstall the NG bond in panel I read mV. That totally odd that would mean no internal bond?. Also my EMP Shield led turned off with my NG...
  • Post in thread: Random power outage EG4 6500 split phase

    I know that this sucks but I also know that I didn't pay the price cost for tier 1 inverters and things happen so hopefully it will work out. I do know that I ran for about 15 months with my 5k growatt inverters without any of these issues but I didn't like the auto-transformer for my neutral so...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    That's definitely what it looks like.
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Has anyone looked into the EG4 6000EX inverters as to neutral-ground bonding? I have 2 in parallel (I have a email to SS to find out if these units are bonded as well)totally off grid and have generator as back up. Just wondering what are my options, I just installed these units 2 weeks ago...
  • Post in thread: EG4 6500EX Generator input

    Gotcha that makes sense, so even if I tweak it down to 3 chargers that's still 54 amps of charge and still would be under my 33 amps. which is more or less 50 to 60amp charge from my inverters with 30 amp input direct connction. I think I might go with this instead. I may get some input from SS...
  • Post in thread: Random power outage EG4 6500 split phase

    Hey JC how are doing. Working on getting it solved with SS.
  • Post in thread: Random power outage EG4 6500 split phase

    Yea I know about the humming but it gets real loud randomly sounds like it's rattling every few seconds. Something like a high power bass in a sound system the rattles the vehicle and this was with very little to no load just idling. Fans were doing there normal idol sound.
  • Post in thread: Ground fault from PV conductors Positive or Negative

    Hello and thank you for the reply,. Poor choice of words, correct not power, ground fault, just voltage reading on conductors to earth. I will elaborate as to how I came about testing on my dilemma. In the summer of this year I was washing off the panels with the water hose in hand and I felt...
  • Post in thread: Random power outage EG4 6500 split phase

    Hello Forum, so I'm still having outages 3 to 5 secs. I've been learning about Solar Assistant and found some interesting info on my slave inverter (pictures attached) I noticed that my inverter 2 show its output is 240V which clearly is not the case, I have checked voltage, and the inverter...
  • Post in thread: Ground fault from PV conductors Positive or Negative

    Another question should I have surge protector (lightning arrestor) at the inverter side? Presently I have them on the arrays and on the equipment side. I also had a 4 gauge bare wire running from the pv to the equipment in ground, I disconnect it when I found this voltage to ground i have read...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Well I'm glad this is all clear now, lol this takes care of at least one of may issues.
  • Post in thread: Random power outage EG4 6500 split phase

    They are connected via parallel, only have main direct connect via 232- usb conversion cable, however I did plug inverter 2 to the pi and had the same 240V, I haven't used usb C to connect since I read many users had issues with the port being fragile. I'm wondering if I ca n have one on RJ45...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Hello Folks, Has anyone remove the neutral-ground screw from the eg4 6000 ex, and possibly have the lactation or pictures of where it is located? Thanks
  • Post in thread: EG4 6500EX Generator input

    @PreppenWolf I seen the video that he says to use chargers instead of a generator. However I don't think he mentioned about a inverter generator whats your opinion on that. My current gen is not inverter based generator and would definitely prefer the gen to inverter hook-up rather than chargers...
  • Post in thread: Random power outage EG4 6500 split phase

    Thank you, On the inverters that I returned to SS I had the update done on both and still had issues, I did check these and the firmware has been updated, I seen you post about the potential you had on batteries and the parallel cables, and from what I tested from earth ground to shield of the...
  • Post in thread: Ground fault from PV conductors Positive or Negative

    Thank you for the information. Apparently some solar distributors don't know this I was 2 months with tech support, engineers and the manufacturer, to figure out what would be causing it and never actually got an answer. And finally got issued rma for the inverters. The only thing that has a...
  • Post in thread: Random power outage EG4 6500 split phase

    That's great, if you don't mind to try something, you might not not like the reading you get, check readings from the positive or negative terminals on PV to earth ground and let me know if you have potential.
  • Post in thread: Random power outage EG4 6500 split phase

    Update: I just connected inverter 2 with a regular usb cable to SA and the crazy voltage deceased to exist, I have 119V on both.
  • Post in thread: Random power outage EG4 6500 split phase

    Yes it will, thanks.
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    Hello yall, I found this video a while back and the way he explains grounding/neutral is very elementary. Hope this helps.
  • Post in thread: Random power outage EG4 6500 split phase

    I do know that I am not the only one having this issue, I also know that this happens mostly on low consumption. Right now as I write this my consumption is 434 watts, and that is higher than normal at night. So far today I have not had issues, today was a very cloudy day and the batteries only...
  • Post in thread: Ground fault from PV conductors Positive or Negative

    It's been operational since October 2021, that's what I thought but when I disconnect the pv arrays from the inverters the voltage goes away, I have been trying to figure this out for several months done all king of troubleshooting. This weekend I am going to start from scratch in the...
  • Post in thread: EG4 6000EX - Double Ground/Neutral

    I will get on that sometime after I have my coffee this morning. As for opening that unit I can't do that due to warranty issues and since SS has not gave me permission to do so.