Are you backing up your entire house panel or just a subset of circuits? I ask because I'm getting ready to install a full stack with gateway for 200amp service. The v2.3 guide states the grid/load terminals will accept wire up to 2/0. In my research 200a should be 3/0 copper. However 2/0 is...
The battery would be connected to the gateway it's just not show in the diagram. I was able to confirm the way this is designed would cause a backfeed to the grid if the battery were to activate, which is a no go.
The electrician decided to backout??!! so I'm going to run this myself.
Hello,
I'm installing an EP Cube Hybrid system to protect an entire load panel. I hired an electrician to run the wiring and the image is what they are proposing to do. I want the gateway to control when I pull from the grid. From the electricians diagram, wouldn't the tap allow the load panel...