One of my combiner boxes keeps throwing the breaker. It's happened multiple times now.
Brand new install - I have 3S4P config on Canadian Solar 420 watt panels. I see the current touching 80amps from time to time. The breaker says
In-80A, I'm assuming that's the trip value. Solar Assistant...
2 LV6548s in parallel. When the loads are less than 60% they operate normally. MPPT current on all 4 inputs is right at the max produced by my panels = approx 17-18amps. I'm nowhere near maxing out this system...
But when the load on either inverter goes above about 60% and the sun is shining...
This brand new dual 8D flooded Battery bank is fine. ANY discharged battery will immediately jump to the ~charging voltage and then settle back down to very slightly higher than the previous voltage if you connect a charger to it for 20 seconds and then disconnect it, which is what this SCC is...
Periodic=repeats= repeats constantly. I.e. sometimes multiple times a second.
you can see the noise in the captured waveform which contains the noise and it coincides exactly with flickering. I expanded the captured waveforms for clarity.
Well, when you capture a waveform that causes led flicker, please post it for all to see. My capture does not show amplitude increase, yet when the noise on the waveform appears, the led lights all flicker. So, either the leds are flickering and inducing the noise (not likely) or the...
They are all rated for 100ah and they all fully hit 100% SOC at about 1pm (assuming Good sunny day), at least as reported by the bms.
I'll change the charge params now and charge at 57.6v @20A and watch what happens. I'm lollygagging in bed anyways, and it should only take a couple hours to...
I totally agree, but we should not be outsourcing so much of this stuff to China....but we do and we get questionable products and components as a result. So, we get cheap, sometimes malfunctioning products billed as quality. It's the price we currently pay.
Breaker is 60A manual. It’s never tripped by itself but I can (and have) tripped and reset it no problem.
I measure only ~12v idle or ~14 when it’s charging at the terminals of the SCC w my Fluke.
Ill try the min/max setting on my Fluke and capture that at our next stop.
I do know that if you provide more than the recommended PV voltage on the pv inputs the LV6048 will generate copious amounts of white smoke.... if you disconnect the offending pv inputs within 5 seconds, your inverter will likely survive like mine did and just heat the circuit board traces to...
I updated to Software version 2022-10-30 a few days ago and MQTT stopped working. I'm monitoring all messages (I see everything but SA) in home assistant, but I see nothing from SA. All states of all inverter objects say "unknown".
Home Assistant version:
Anyone else having this...
So I got to the bottom of this confusing mess by doing a full capacity test on the 4 x 100Ah pack. It turns out that the batteries have a full 100Ah of capacity each, and the params in the battery are incorrect. After a full charge to 54.8v and then a full discharge down to 48v (leaving 10%) I...
Anyone know of a way to get the last error code thrown by any inverter via MQTT? I have home assistant working very well, but I don't see error codes exported in any objects...
Jeff
On standard PV wire?? I don't think that's a good idea... However, I'm thinking of running 6 awg to the inverters or 2 pv wires each on +/- to the inverter.
One of my LV6548 inverters mc4 connectors failed and I got 0v on PV1. Voltage on the incoming wires is fine. Anyone else had this happen? This is a REALLY bad design on an otherwise great inverter.
I just ordered a couple of these to bypass the mc4 connectors and hardwire directly to the...
Interesting. I'm sort of leaning toward this config:
An alternative config I've considered is paralleling the outputs in 180degree configuration, providing 240v @100A in total, and then running 240v 50A circuits to each of the sub panels.
then, even if one unit failed, I still have the other...
So I did measure 0.5v +/- .2v across the DC breaker. And its contacts feel way warmer than they should at it's 80A rating. It probably is worthwhile to use an industrial breaker here. I got this one from the vendor who sold me the SCC, but clearly it's not up to the task. I'll bypass it when the...
Controlling SA via MQTT was just released. It takes some careful setup but the guide is pretty complete. I'm planning on testing it when I have some spare time.
Start here and get this working first, then use Node Red to send control messages via MQTT...
Lol! Pbms is a windows application written by one of the bms vendors that lets you talk to your bms and look inside the batteries. And, Yeah, I had a stroke 6 yrs ago and switched to MacOS and I never looked back.it's shocking how easy it is to use iOS and macOS. I was/am about as expert as it...
Im not sure where the bug is. No way to roll back SA versions... and I'm in the middle of climate/Tuya/ESPHome hell or I'd roll back HOME ASSISTANT and see if that was it...
I agree, lots glossed over in examples. This is a great question best asked in the home assistant forums. I'm no Node Red expert, and youll get Node Red experts there. You've got all the basics, now the specifics. If this is the message received via Mqtt from SA, you'd want to send the same...
Ok, it's like watching paint dry, but I think we've all done it. The capacity test revealed a full 382ah was taken out of the battery pack over 8 hrs. 2 of the 4 packs shut down when the lowest cell voltage in each pack reached 2.5v and that's when I stopped the test. SOC was 0% for about 1:10...
FWIW, You are living my nightmare. I'm seeing the exact same thing, although I'm using 2 8D flooded cells, not lithium's. My EPEVER tracer 60A will charge @20A or so for 20-30 seconds and then just shut down for no apparent reason, then start back up charging again a couple mins later. And cycle...
I suspect I have a low voltage condition. Does anyone know the MINIMUM PV voltages required? I'm loathe to get up on my RV roof and rewire my panels, especially since the wind is blowing at 30-40 mph right now.
The controller cycles from charging to off after about 20 seconds, resets after...
I started with battery ID 1 and SA sees all 4 batteries and all of their params. It's just the mqtt data in home assistant that isnit flowing from sa to home assistant for batteries 2,3 &4. Home assistant has each battery listed, just no data "unknown" for each attribute. I tried your steps...
THAT oddity is our lovely Solar Assistant averaging my THREE inverters. It has ZERO bearing on reality- I've reported it to Pierre at SA so he can find a solution. As I said, inverter #3 is for battery charging ONLY. I have it added to SA just so i can see how much power is being generated...
I will be in a couple of weeks - my pump is 240v@20A. Ran my entire shop all day today including a Frigidaire 25,000 btu ac unit Entirely on PV. Both units hummed right along at 16% & 30% capacity. A slight flicker on all my overhead LED lights when the compressor kicked on, but not every...
The Fluke meters are my go to for clamp & multimeters. Got my first one in electrical engineering school 40 odd years ago. They're pricy tho. Will has one in his website he recommends
https://www.mobile-solarpower.com/tools.html...
Nope, that's not it. The battery is quite discharged @ 12.22v - I ran the whole coach all night and started from 13.5v last nite. And if I fire up the genset, it charges at 100A continuously without going to float mode. Fully charged, the battery is at 13.7v.
So... the SCC should remain ON...
Well, it seems to work using these settings connecting to the SA mqtt server OR the Mosquitto server I have running on HOME ASSISTANT
And hitting the inject button definitely changes it to Utility.
However, after a few seconds, it switches back to Solar/Battery/Utility as you can see on...
"with the wiring".... actually i would rephrase. The wire is fine... "How it's wired" is the issue. I think I need to move one parallel string to a different combiner box to balance the loads. The "way" it's wired is causing too much current to flow through the breaker, thus tripping it.
I posted this in the tech support area but got no responses.
Any help appreciate... this is driving me nuts.
https://diysolarforum.com/threads/2-lv6548s-strange-behavior-when-under-loads-60.45372
New install... I just got the equipment today.
I have 2 LV6048 inverter/charge controllers and 4x100ah LifePO4 48v batteries. And 24 420w panels with two 6x2 combiners.
https://watts247.com/manuals/mpp/LV6048%20split%20phase%20manual-20201120.pdf
I am powering them with a 100A sub panel w 40...
I'll check tomorrow at peak production... it's on the down swing of production right now - 6:30pm. I'll also measure the actual DC current on each leg of the combiner box inputs at peak product (1pm or so) as well as the output.
canadian solar 420watt panels.