  • Post in thread: 4 EG4 6500ex flickering lights on low loads only

    We have an offgrid 8k sq ft house (4ksq ft of it is basement We got 12 felicity solar batteries 10kwh each 6 eg 4s 6500. We were told not to put more than 6 batteries in parallel. We have two sets of 2 victron bus bars connected to 6 batteries each. Invertor 1, 2 and 4 (all sp1) are going...
  • Post in thread: My experience large offgrid EG4 6.5kwh with felicity solar batteries, 60 solar panel system

    I figured I write up our experience. Shout out to kodi at signature solar design team in helping us design this. We have an offgrid 8k sq ft house (4ksq ft of it is basement for wine) in temecula it would cost upwards of 200k to bring grid power so we opted to do it off grid for now. We got...
  • Post in thread: Growat SPF 12000T DVM-MPV Only gets 30amp charge from generator

    I dont think so. Reading the ac input off the inverter
  • Post in thread: Growat SPF 12000T DVM-MPV Only gets 30amp charge from generator

    I don’t think the issue is the batteries. It cant be coincidence that the growat default ac input is 30amps and that is what it is showing . Somehow the changes we made on the settings are not being executed.
  • Post in thread: EG4 6500 causing flickering lights when on battery power

    We have an offgrid 8k sq ft house (4ksq ft of it is basement We got 12 felicitysolar batteries 10kwh 6 eg 4s 6500. We were told not to put more than 6 batteries in parallel. We have two sets of 2 victron bus bars connected to 6 batteries each. Invertor 1,2 and 5 are going battery bank 1...
  • Post in thread: Growat SPF 12000T DVM-MPV Only gets 30amp charge from generator

    Thank you for your replies. My main concern is ac input is only showing 30amps which is the default setting when the generator is capable of much more. I will need find how much amp is going into the battery and use the conversion factor. I did speak with signaturesolar and I may need to...
  • Post in thread: EG4 6.5kw adding two inverters better to move solar?

    I have a large offgrid home, We have two battery banks of 60 kwh. I have two panels in the house which are seperated. Currently I have total 4 eg4 6.5kws invertors 2 going to each house panel in split phase. Each invetor pair that is in split phase draws from the 2 battery banks so that they...
  • Post in thread: Growat SPF 12000T DVM-MPV Only gets 30amp charge from generator

    I have growatt SPF 12000T DVM-MPV connected to 3 phase old diesel generator 80kw 250amp(we connected 2 phases). I set all applicable settings to at least 80amps but growatt still showing 30am ac input. We have 3 felicity solar 10kwh batteries in parallel which can take 120amp charging. What...
  • Post in thread: Growat SPF 12000T DVM-MPV Only gets 30amp charge from generator

    Yeah i set both of those higher. I think it just needs to be reset for those changes to actually take affect. This is in a remote location so once I go back, I will try disconnect reconnecting power and see if it fixes it. I report back.
  • Post in thread: EG4 6500 current sharing cable gauge

    Does anyone know the gauge of the current sharing cables that come with the EG4. Mine are not long enough and I need buy the wires and redo it.
  • Post in thread: EG4 6500 causing flickering lights when on battery power

    I have tried one before and latest. The battery bank is too much to have on one bus bar. I did put all sp1s on one bank and all sp2s on the other bank. The design team suggested having each leg go to different battery bank as to not over use one. 1/3 dont have power sharing and they have...
  • Post in thread: felicity solar LPBF48200 10KWH 6 in parallel to a bus bar do i need the bms connected

    I have bus bar with 6 felicity solar 10kwh. I can connect each bms together to be in "parallel". However the bus bar is connected to each battery individual with same length wire. My question is: Is there any advantage to connected the bms together. What i am worried about that it just...
  • Post in thread: Felicty solar lpbf48200-p putting more than 6 in parallel

    We are a building a large off grid system. We have 4 eg4 6500 inverters in parallel, 12 lpbf48200-p felicity solar batteries each 10kwh, and 60 solar panels each at 400watts. In discussing with signaturesolar, they indicated it is better if we could make one large battery bank connected to all...