Recent content by karthik_bkv

  1. K

    Cell Over Charging in JK BMS

    @AshleyL , this works. Now the cells are balanced at 3.5v, no OVP is triggered. Working as expected Thanks Buddy!! For your suggestion 😉
  2. K

    Cell Over Charging in JK BMS

    Changing the Cell will help to fix this?
  3. K

    Cell Over Charging in JK BMS

    Current status, with no Solar Charge, seems the cell are balanced, the Voltage difference between the cells are reducing gradually.
  4. K

    Cell Over Charging in JK BMS

    I've changed the Charging voltage to 27.4v let see if it behaves similar tomorrow. Thanks for your input.
  5. K

    Cell Over Charging in JK BMS

    This is my current settings
  6. K

    Cell Over Charging in JK BMS

    Yes, happened exactly same as shown in the video! Cell 8 goes upto 3.700v, all the cells in the battery bank is new Is this a BMS failure?
  7. K

    Cell Over Charging in JK BMS

    Today's value, the cell voltage difference is too high at this point, before that the voltage difference is 0.05V. Can anyone help me on this?
  8. K

    Cell Over Charging in JK BMS

    Thanks for letting me know, I will make the changes as suggested. 😊
  9. K

    Cell Over Charging in JK BMS

    Cell imbalance only on full charge, not on discharge or 80% charge
  10. K

    Cell Over Charging in JK BMS

    Charging voltage set in MPPT charge controller 27.6v
  11. K

    Cell Over Charging in JK BMS

    Hi Ashley, Thanks for your response Yes the cells were top balance before putting them, BMS is 0.6A balancer
  12. K

    Cell Over Charging in JK BMS

    Hello All, When charging the 8s 100Ah lithium-ion battery with a JK BMS with an active balancer, it's noticed that the cell voltage difference is too high, leading to 2-3 cells being overcharged and triggering a cut-off in the BMS. Is this expected behavior, and are there any solutions to fix...