Unfortunately, 18 panels is not not a good mix for peak voltage.
The controllers can't experience more than 250V in any conditions...
-
M
Thank you very much for the info. It's more than I've gotten over the last 5 days of googling the subject.
Do you think I should put any...
-
M
Also....
The panels will be roof mounted with the controllers in the bunker. Approximately 45ft from SCC to the panels and another 33ft...
-
M
We bought the Sungoldpower 18kw kit with 18 panels, 2) SGC4825100A SCC's, 18kw 240v inverter and 4) 48v 100ah rack batteries...
That...
-