Recent content by Mtour

  1. M

    Lister C/S with inverter generator hardware?

    I have a Lister 6/1, it powers a two Delta q 48v 18ah chargers, roughly 2000w. The delta q chargers do not care about frequency nor voltage, the Avr in the generator keeps the voltage close to 240vac and the hrz fluctuate between 55-60. Rpm with no load is 660 and under load its around 640rpm. I...
  2. M

    Big ole batteries!

    If you have a 200w+ solar panel kicking around you could connect it direct to a single battery. Leave it outside in the sun and watch the sg's over time, it will take along time to get the sg's up. Do not worry about hooking a 39v panel to a 2v cell, that battery will bring the solar panel down...
  3. M

    My 64kwh BYD battery bank

    I'm seeing 2.7kwh per pack usable..cycling 3.06v-3.4v..these days I a pulling over 50kwh nightly on sunny day running a couple heat pumps...the byd's have been very stable and I have seen no degradation on the trimeric meter over the past year of daily cycling.
  4. M

    My 64kwh BYD battery bank

    Nice work...I am running a similar wall and find the batts like 55v three hour absorption, 53.8v float..
  5. M

    Understanding MPP Solar charge settings for LifePO4 batteries

    My surplus Byd batts will absorb 3-4 hrs at 3.4v per cell, they will accept an additional 10% charge once they hit the 3.4v per cell at absorption.
  6. M

    Will the LV5048 only charge from grid in bypass?

    Anyone know if it is possible to get the Mpp Solar LV5048 to charge from grid and not be in bypass mode. Trying to charge bank with a diesel generator loaded to 90% and have the house running on inverted power so as to not overload the generator with house loads. thanks...
  7. M

    BYD Battery - Charge low cell

    I used the same screws as above, works really well.. I added headways to the cells that are lower in capacity, then paralleled the cells with fused interconnections. After all that I still only charge to 95% which my batteries hit at 54.4v at 2-5hrs at absorption , if the batteries are fully...
  8. M

    BYD packs — one year on — survey

    I am finding my BYD's to be very stable after doing the fused cell interconnects and headways, packs stay within 50mv on the knees... I have been running the cells between 3v-3.4v per cell, and pull +-20 kwh daily.. The main thing I find with these byd's is that they need time at absorption...
  9. M

    Understanding MPP Solar charge settings for LifePO4 batteries

    As of now my voltages are 54v float and 54.4v bulk... I got to 100% charge the other day for the first time in a month, been sitting between 30-85% soc since late September. In the summer months I run 53.6V float and 54.2v bulk as I am at 100% soc daily by noon most days.. My bank of batteries...
  10. M

    Grade A cells, first charge a cell drifts 0,08V. Would you accept this ???

    You could try arranging them In a different order and see if the imbalance follows the cell...
  11. M

    I'm doing something wrong but.....BYD modules/balance charging settings using ISDT Q8?[/frustration]

    As stated above it is a Lifepo4 battery... I have read a few people that received packs with 80-90% capacity, but the vast majority are getting 60% of stated new capacity (+-110ah). These packs seem to be happiest between 3-3.45v per cell, trying to run them out of this range tend to lead to...
  12. M

    Understanding MPP Solar charge settings for LifePO4 batteries

    The charging led on the lv-5048 dash will flash when in bulk and stay on when in float mode. Could the spike in charging current be following a load on the inverter in float mode..
  13. M

    Understanding MPP Solar charge settings for LifePO4 batteries

    Lipos are a whole different animal 5c charge rates and 60c discharge...
  14. M

    Understanding MPP Solar charge settings for LifePO4 batteries

    This is what I find as well, I can get to 98% soc @ 3.37v per cell but it will take 4-6 hours of absorbtion, absorbtion will start at around 90% soc. If I were to charge to 3.65v I would be able to get from 90% soc to 100% in no time, but I would start to get imbalances(40-80mv) and could...
  15. M

    Understanding MPP Solar charge settings for LifePO4 batteries

    Sounds like a good plan to play it safe and not try to get every last amp.. In the summer I had the float at 53.8 and bulk at 54v and 1 hour absorbtion... I would be a float about 11am every day.. Now with the limited sun I have float at 54v and bulk at 54.4 with 4 hours absorption.. I have...