New Growatt hybrid inverter SPH10000TL- HU-US split phase

Let's go!!

One thing I found out that I really like is that even though it's only a 10kw inverter, it can use 10kw of pv to power loads and up to another 5kw to charge the battery!

That's awesome.

That's something I'll consider down the road, initially I'm probably under-paneling, at just over 20kw worth of panels for what will be 2 inverters.
 
Here is one
Thanks, it's got to be a V1 because the nameplate says it only does 5,000 watts backup power. V2 & V3 do 11,400 watts backup power as listed on nameplate.

Question: when did you purchase from signature Solar? They have stated that they have sold nothing but V3 inverters since September of last fall.

Its also odd that the part number does not match any of the part numbers for these inverters I was given last year.
 
Thanks, it's got to be a V1 because the nameplate says it only does 5,000 watts backup power. V2 & V3 do 11,400 watts backup power as listed on nameplate.

Question: when did you purchase from signature Solar? They have stated that they have sold nothing but V3 inverters since September of last fall.

Its also odd that the part number does not match any of the part numbers for these inverters I was given last year.
Purchased Sept 2022. Didn't realize the newer ones can do full backup power.
 
Growatt told me on the phone that it can accept up to 80a of Gen input

When the generator is connected and charging the battery it's also passing through power to support the backup loads so the inverter max output of 10kw does not apply.
Anyone figure out the AC coupled limits for this unit yet?

Breaker recommendations on grid and load side are both 80A. If you can get 41.6A via PV, and you want to stay <1.25x breaker rating, that leaves 64-41.6=22.4A (5400W)

6AWG wire is specified, which even in copper, which looks like max 75A. So I don't think there's room to go higher than 80A on the breaker.
 
Anyone figure out the AC coupled limits for this unit yet?
I believe the ac couple limit for “any” Growatt would be less than or equal to the output capability of the Growatt grid forming inverter. Give the Growatt white paper I link below a read. It for the SPF but I believe it is applicable to all Growatt ac couple capable inverters- I have found it’s description of how their ac coupling works is spot on for the MIN-US inverters. Specifically, page 4 “In the application of micro-grid without grid input, the AC output of the SPF 3000-6000T HVM-G2 inverter can serve as a voltage source to connect grid-tied inverters and loads. In this scenario, the power of the grid-tied inverter must be less than or equal to the power of the SPF inverter.”

blob:https://community.growatt.com/562792fe-efef-4a14-8172-4730007a7b06

Link doesn’t work, go to link below and search for “

AC_Coupling_frequency_shifting_technology_of_SPF_3000-600”​

 
I believe the ac couple limit for “any” Growatt would be less than or equal to the output capability of the Growatt grid forming inverter. Give the Growatt white paper I link below a read. It for the SPF but I believe it is applicable to all Growatt ac couple capable inverters- I have found it’s description of how their ac coupling works is spot on for the MIN-US inverters. Specifically, page 4 “In the application of micro-grid without grid input, the AC output of the SPF 3000-6000T HVM-G2 inverter can serve as a voltage source to connect grid-tied inverters and loads. In this scenario, the power of the grid-tied inverter must be less than or equal to the power of the SPF inverter.”

blob:https://community.growatt.com/562792fe-efef-4a14-8172-4730007a7b06

Link doesn’t work, go to link below and search for “

AC_Coupling_frequency_shifting_technology_of_SPF_3000-600”​

the first link is broken
 
I hope to make a couple of videos if I actually get one. Ordered it a week ago. Still hasn't shipped
I'm pretty pi$$ed to say the least.
Bummer, it sounds good on paper but I'd like to see how the reviews are. I'll look forward to watching your video when you make it.
 
Bummer, it sounds good on paper but I'd like to see how the reviews are. I'll look forward to watching your video when you make it.
I know right? They all sound good on paper but working in the real world is where the wheat is separated from the chaff, so to speak.

What I'm most anxious to test is the self consumption mode. If this mode works like I think it should it will be a game changer for the off grid(but grid available) community
 
It looks like it's on the California Solar approved list as of May 21st, 2024, pulled from the excel spreadsheet on the website. Perfect for us in restrictive areas. Now if only someone can get a hold of one and show it off to the rest of us. Capture.JPG

Capture2.JPG
 
It looks like it's on the California Solar approved list as of May 21st, 2024, pulled from the excel spreadsheet on the website. Perfect for us in restrictive areas. Now if only someone can get a hold of one and show it off to the rest of us. View attachment 218989

View attachment 218990
Awesome! Thanks for posting.
If that's the efficiency on battery it would be amazing
 
Looking forward to much more detailed info on this inverter.

No 200a grid passthrough on the backup loads vs 18kpv or sol-ark. Will it only pass through 10kW (41.6A)? If you parallel 3, I guess you can get 120A. Can you parallel more than 3?

What's the max AC coupling on the Gen input? I see recommended breaker of 80A and error code W27 is described as "generator power exceeds 11kW for more than 2 hours."

I really like my 4x Min11400. Such great value.
Referencing the attached image, my plan was to only use the On-Grid/Home Load with the CTs for zero export. But your comment on Pass-through limitations for the Backup loads made me think, maybe the Home Load is not powered in a Grid Outage?

Does anyone know if this is the case based on other Growatt units?

Does the Inverter internally disconnect the On-Grin/Home Load line when a power outage is detected? With the CTs installed it should be able to limit any power flowing into the Grid.
 

Attachments

  • Screenshot 2024-06-01 at 1.01.37 PM.png
    Screenshot 2024-06-01 at 1.01.37 PM.png
    301.3 KB · Views: 12
Referencing the attached image, my plan was to only use the On-Grid/Home Load with the CTs for zero export. But your comment on Pass-through limitations for the Backup loads made me think, maybe the Home Load is not powered in a Grid Outage?

Does anyone know if this is the case based on other Growatt units?

Does the Inverter internally disconnect the On-Grin/Home Load line when a power outage is detected? With the CTs installed it should be able to limit any power flowing into the Grid.
Home loads (grid line)are required to be disconnected in the event of a grid outage. All hybrid inverters do this.
 
Last edited:
It looks like it's on the California Solar approved list as of May 21st, 2024, pulled from the excel spreadsheet on the website. Perfect for us in restrictive areas. Now if only someone can get a hold of one and show it off to the rest of us. View attachment 218989

View attachment 218990

It is just below the 10kW-AC cutoff (for one) where PG&E starts getting salty and demanding for some system configurations. If you need more than one and are in a similar jurisdiction you need to confirm the PRD PCS certification situation.
 
Referencing the attached image, my plan was to only use the On-Grid/Home Load with the CTs for zero export. But your comment on Pass-through limitations for the Backup loads made me think, maybe the Home Load is not powered in a Grid Outage?

Does anyone know if this is the case based on other Growatt units?

Does the Inverter internally disconnect the On-Grin/Home Load line when a power outage is detected? With the CTs installed it should be able to limit any power flowing into the Grid.

Out of curiosity, what manual did you screen shot that from. I don't think I've seen a manual with the generator port shown being used as a smart load.
 
Interesting, I guess I just never noticed it. Perhaps I could use that for a water heater function in the future (although with my current water heater setup, its not really needed)
Tbh I'm not really sure what people use smart load outputs for
 