I have this inverter.

I can answer all your questions. I have been running this inverter batteryless without grid and with grid.

First let me tell you I am very happy so far with it .

Yes when you have Grid mixed with AC grid , it shows false readings of feeding the grid. But a bidirectional smart energy meter shows otherwise . 0.00000kwhr. So the inverter is never backfeeding. Although the monitor program says it does.

I agree with what other people say about voltage.

I have 340V DC VOC from the panels , and they are suffering under load when its REALLY cloudy. Basically , the MPPT will go down to 120V under load, since this is the minimum operating voltage , to try to extract maximum power ( ampers ) but this is a "bad" zone. More voltage = better. I am not sure how exactly the MPPT works to favor the direct DC to AC but what I know is that it works really good when its sunny , not so good when its VERY cloudy. When its normal cloudy its fine with my 340V VOC.

I mean it works really good.

Also dont listen to people that say it doesnt work batteryless or it's not supposed to work like that.

I have tested it batteryless without AC and if your loads are fine under the cloudiest time, the inverter will work fine and as intended.

So example : Put 300w loads , with 3.1kw of solar panels flat on the ground , they switch on in the morning , run for the whole day fine and switch off when it gets dark. IT WORKS FANTASTIC AND AS INTENDED . I know though you will be wasting a lot of power this way but there are special applications where this makes sense. Worst case scenario is the inverter will cycle on/off.

Obviously if you are powering a home , you would need batteries to even the cloudy times and not lose energy but trying to have always the load at the minimum power production of the day ( like 300w from 3.1kw flat panels in November ) . The whole point is that you can mix with AC and avoid batteries.

I don't use batteries and it works FINE and as intended.

It's great.

The only problem is the N/G bond when you lose the AC in , which is solved with the dry contacts' external grounding box.

As people said , I would recommend at least 340V VOC like me , even more if you live in a very cloudy place . I would try to hit the 450V ideally. As I said when its really cloudy , the MPPT is kind of struggling.

Let me know if you have any questions .

Cheers.
If this inverter works for you both with PV without the grid and without batteries, can you tell us how you set the programs?
I have 300Voc and unfortunately the inverter (SMG II 3.6 kW 24V) does not want to start without the mains, because I do not have batteries yet.
Thank you for your help.
Best regards,
Jacek.
 
Have you tryed SBU mode, i only tryed without bateries with 100w wolfram bulbs and it worked.For runing stable you need some battery pack.
 