EG4 6000xp and PowerPro indoor battery charge questions

kampto

New Member
Joined
Mar 6, 2022
Messages
44
I commissioned my 6000xp and its connected to eg4 powerpro battery a month ago. EG4 monitor is set to "Lithium" battery and com set to "0:EG4" so im using SOC% and not setting absorb/float voltages. The online XP Monitor can read the battery stats. Where are the charge settings coming from, the XP or the powerpro? Because the powerpro document recommend settings are 56.2v bulk/absorb and 54v float. Buts it not doing that, is maxing out at 54v and floating at 53.4v and saying its 100% SOC. So 54V is now 100%?
1718220092195.png
 

Attachments

  • 1718220169980.png
    1718220169980.png
    56 KB · Views: 6
Last edited:
You might need to top balance the battery cells. I would recommend charging by voltage for a few days then switching it back to SOC. You would have to set the battery type to "Lead-Acid" and set the absorb/bulk to 56.2, float to 54V and the low DC cutoff to 47V.
 
You might need to top balance the battery cells. I would recommend charging by voltage for a few days then switching it back to SOC. You would have to set the battery type to "Lead-Acid" and set the absorb/bulk to 56.2, float to 54V and the low DC cutoff to 47V.
In progress, doing it remotely!
 
OK, doesn't seem to be working. On 2 separate 3 day long stents I set up 6000xp as Lead acid to top balance, bulk 56.2v and Float 54v. It followed the lead acid voltages just fine. When going back to Lithium-SOC mode its still barely getting over 54v for bulk and floating around 53.5v. So how to run in Lithium-SOC mode and get the recommended 56.2v bulk and 54v float?

1718996983422.png
 