I have an 18KP invertor with 16kw solar and 12 48v lifepro batteries. Originally installed with only 6 battery pack and every thing worked great. We would run the batteries down to 30% and they would all charge to 100% with no problems. Added the second bank of 6 batteries to the system as we were going to add extra load and were worried about being short of power overnight. Everything was fine the first day of operation. Bank1 was charged to 95% and Bank2 was only at new battery charge of 50%. Ran the banks down to 15% and let system charge but could only get 83% charge. Thought that was because of the extra load to get bank2 up to bank1. The next day we were at 40% to start charge and could only get to 90% charge. Then again from 40% to 89%. That is when I started to look at the battery communication information and all batteries in bank2 were balanced at 99-100% but bank1 was all over the place from 70-83%. Now the question I have is that if the battery that shows 100% has all the cells within 3.337 to 3.338 at 53.6 volts then how can a battery at 70% show cells at 3.334 to 3.337 at 53.6 volts. Am I missing something here? Does this just mean that the bms has drifted and the batteries are all ok or do I have to worry that I am having battery failures?