Brandontoron,
No, you are gonna need a second SCC. Look at the specs for your scc:
HQST 40Amp MPPT Solar Charge Controller
- Battery voltage: 12/24V
- Max PV Input Voltage: 100V(25℃);
- Charge current: 40A
- Max. PV input power: 600w/12v; 1200w/24v
So the max PV solar panel input is 600w. And that is 40A of OUTPUT POWER TO BATTERY, not PV input.
You have 800W if one panel, and 740W of the other. Your SCC doesnt even handle a pair of them. You can't even series 2 of them without exceeding the 100v max in cold weather.
If you wired each pair in parallel:
Canadien 800w total, 52.3voc, you would lose 1/4 possible power on that hqst alone. Now they probably wouldnt really produce 800w, but might do 700 on good days.
1540W total for all of them, theoretical. At 15v to 14v lithium charge rates, thats 113 to 130A needed for a SCC!
If you had a 24v battery pack, you could do twice the watts.