I have an lv2424 with 2) 24v 100ah batteries in parallel. 9 230 watt solar panels wired in 3s3p. Each solar panel has a ocv of 37, so that puts it at 111 ocv, which is under the max voltage of the lv2424.
I also have a 4550 watt inverter generator, that I run to the ac input on the lv2424, and I have the max set at 60amps (that's 60 amps at 24 volts) from the generator to the lv2424 to help out.
The problem is that I am getting a fault code 07, which appears to be overload timeout. If I unplug the generator, I do not get the fault.
Power consumption is 2100 watts when it gives the fault. Any ideas of what is causing that fault?