diy solar

diy solar

Will generator work with Growatt?

Has any one experienced a similar problem with the growatt dry contacts closing as it should when voltage low but as power is introduced to the inverter from the generator it opens the contacts and stops the generator. If so, please let me know the fix. Thanks
 
Has any one experienced a similar problem with the growatt dry contacts closing as it should when voltage low but as power is introduced to the inverter from the generator it opens the contacts and stops the generator. If so, please let me know the fix. Thanks

Can you share your settings of 01, 11, 12, 13, 14, and 24? I assume you want the dry contacts to start and run the generator when the battery is low, charge the battery, then shut off?

The dry contacts operate on a combination of these settings, and I think we can find what needs to be adjusted to make it do what you want.
 
Thank you for such a quick reply! Yes on low voltage I want the generator to start charge and run the house. It starts but as soon as it receives power from the generator it stops. I shut off tge generator breaker and tested and the contacts remained closed, only when it receives power does it shut off the generator.
Settings below
01 sol
11 20A
12 45V
13 50V
14 C50
 
I'm following with interest, as I don't want a dedicated back up or diesel generator. I have a cheap hyundai 3500 peak, 2800 running remote start inverter gen. I have to admit it has been a little tank. We have built 3 cabins with it as our only power source for work, 1/3 hp well pump, and other power. I'm now considering 1 of the 2 below, as I have propane roughed in for a gen, and wall heater to our solar shed, from our big tank.

The 4500 uses .44 gallon per hour +- @50% load
The 9000 has 120 and 240v, and uses 1 gallon per hour +- @50% load
I am trying to determine the real minimum load that I might be able to get away with. I'm not there yet, but I think I can rig up the 9000 to use slightly more than the 4500, in best case scenario with less load required, and still have the extra power, and 240 for a small welder when I need it.

My #1 priority is using the least amount of LP as possible, while having adequate back up, but the extra power would be nice. I'm going to do some math but I might buy them both, test real world then sell the one I don't want. If Lp consumption can be brought within 20% +- it will be the 9000.

FYI 2 friends have similar units to the 4500, sold as Westinghouse. Based on their experience, I think I'll avoid it.


 
Thank you for such a quick reply! Yes on low voltage I want the generator to start charge and run the house. It starts but as soon as it receives power from the generator it stops. I shut off tge generator breaker and tested and the contacts remained closed, only when it receives power does it shut off the generator.
Settings below
01 sol
11 20A
12 45V
13 50V
14 C50

50v is pretty low in setting 13. When the generator starts and battery charging begins, the voltage of the battery will go above 50v right away with most types. What battery chemistry are you using, and what are your settings for 5, 19, 20, 21? A few proper adjustments will resolve your issue. Also, I assume setting 24 is set to "dis" - right?
 
I'm following with interest, as I don't want a dedicated back up or diesel generator. I have a cheap hyundai 3500 peak, 2800 running remote start inverter gen. I have to admit it has been a little tank. We have built 3 cabins with it as our only power source for work, 1/3 hp well pump, and other power. I'm now considering 1 of the 2 below, as I have propane roughed in for a gen, and wall heater to our solar shed, from our big tank.

The 4500 uses .44 gallon per hour +- @50% load
The 9000 has 120 and 240v, and uses 1 gallon per hour +- @50% load
I am trying to determine the real minimum load that I might be able to get away with. I'm not there yet, but I think I can rig up the 9000 to use slightly more than the 4500, in best case scenario with less load required, and still have the extra power, and 240 for a small welder when I need it.

My #1 priority is using the least amount of LP as possible, while having adequate back up, but the extra power would be nice. I'm going to do some math but I might buy them both, test real world then sell the one I don't want. If Lp consumption can be brought within 20% +- it will be the 9000.

FYI 2 friends have similar units to the 4500, sold as Westinghouse. Based on their experience, I think I'll avoid it.


I’m not sure what kind of system that you have. I have a 48v 3500w all in one unit. I use it in a travel trailer so incoming power is limited to 30 amps 120v. I am able to use a predator 3500 (3000 continuous watts)! By setting the charge rate low and limiting my loads or limiting my loads to 800 watts till the batteries are charged I can use it with no problem.
I don’t know how far north you are but starting a lp generator in subzero weather (Fahrenheit) is virtually impossible and smaller lp tanks can “freeze” in similar temperatures causing other problems. Just thought I would let you know in case you live in a climate cold enough and haven’t done anything with lp in those temps.
 
Thanks Bobert. The generator will be inside and warm, exhausted outside. I have a 500 gallon tank, full and ready to go. everything is roughed in. We've been using 20 to 100lb tanks for many years
 
Thanks Bobert. The generator will be inside and warm, exhausted outside. I have a 500 gallon tank, full and ready to go. everything is roughed in. We've been using 20 to 100lb tanks for many years
Good deal I was hoping you had a setup like that.
 
My generator charges my 2 lithium 24v 100ah ampere batteries through my 24v 3000k growatt. I have a 3500 predator from harbor freight. Just gotta remember to change the oil often if your running it a lot like i do. Hope this helps.
i have the same generator (the quiet predator 3500) but will be using it will the growatt 48v 3000. do you have to physically turn on the generator or can the inverter trigger the electric start? also are there any setting to the ac charging amount or anything that youd recommend?
 
i have the same generator (the quiet predator 3500) but will be using it will the growatt 48v 3000. do you have to physically turn on the generator or can the inverter trigger the electric start? also are there any setting to the ac charging amount or anything that youd recommend?
Most AIO units that I know of have a relay that can trigger automatic start on a generator however the predator 3500 inverter generator does not have auto start. There is an aftermarket remote start available but I don’t know if it is practical be modified to operate off PV a relay instead of a fob or not.
 
I think there's a real advantage to using a dedicated charger hooked to the generator rather than running through the inverter. If you use the inverter you have to set the charging amps low enough so that the loads + the charger don't stall the generator and with changing loads there are times when you could be putting more power back into the batteries but can't unless you change the charging parameters.

With a separate charger you can maximize the charging amps and fill the batteries up probably faster and with less wear & tear on the ginny and maybe use a little less fuel to boot.
 
I'm trying to use an Ecoflow DeltaPro Europe Edition as generator for Growatt SPF5000 48v.
- DeltaPro can output 3600W at 230V/15A.
- Growatt has a 3KW PV solar string but no batteries
- I don't want to invest in a dedicated set of batteries for Growatt
- I want to use DeltaPro battery/PV charging as Utility for Growatt

When i'm connecting DeltaPro AC-out to Growat AC-in is working fine.
But the minute I'm adding a 1KW/2KW consumer on Growatt AC-out ... Growatt is overloading the DeltaPro.

I've tried multiple combinations for settings:
01 : SOL/SUB
02 : 10A/20A
03 : APL/UPS/GEN
11 : 10A/15A

Any suggestions are appreciated.
Thank you.
 
I'm trying to use an Ecoflow DeltaPro Europe Edition as generator for Growatt SPF5000 48v.
- DeltaPro can output 3600W at 230V/15A.
- Growatt has a 3KW PV solar string but no batteries
- I don't want to invest in a dedicated set of batteries for Growatt
- I want to use DeltaPro battery/PV charging as Utility for Growatt

When i'm connecting DeltaPro AC-out to Growat AC-in is working fine.
But the minute I'm adding a 1KW/2KW consumer on Growatt AC-out ... Growatt is overloading the DeltaPro.

I've tried multiple combinations for settings:
01 : SOL/SUB
02 : 10A/20A
03 : APL/UPS/GEN
11 : 10A/15A

Any suggestions are appreciated.
Thank you.
I’m not sure what you are trying to accomplish. Why don’t you use the eco directly to power your load?
 
DeltaPro is a portable grid-centric back-up solution with week solar charging potential.
I'm using it as a backup with success, but it has many limitations.
What I need now is a solid off-grid solution with a more capable solar charging potential.

Let's talk more about solving technical problem i'm facing, rather than questioning ideas.
What i'm trying to accomplish is very clear : using DeltaPro as Utilily for Growatt SPF5000 ES
Why ? Because of many personal reason that I consider having value for me.
 
DeltaPro is a portable grid-centric back-up solution with week solar charging potential.
I'm using it as a backup with success, but it has many limitations.
What I need now is a solid off-grid solution with a more capable solar charging potential.

Let's talk more about solving technical problem i'm facing, rather than questioning ideas.
What i'm trying to accomplish is very clear : using DeltaPro as Utilily for Growatt SPF5000 ES
Why ? Because of many personal reason that I consider having value for me.
One problem is that your growatt is designed for nearly twice the amperage than what the eco flow can provide. I would suggest that to get it working you connect it to grid power at the amperage specification listed in the manual and then experiment with the settings till you find what is causing the unexpected power consumption. Remember an AIO only passes through ac power it doesn’t subsidize it so without a battery you will be either running completely off of the solar or completely off of the ac. I suspect that in order for the inverter to work “directly” from solar it must have some sort of a capacitor involved that may be overwhelming your eco flow. If there is a setting that prevents this you will still have to factor in the power consumption of the growatt itself when it switches to ac. The reason I was questioning what you are trying to accomplish is that I was wondering if it is even technically possible to do what you want with an AIO because of how they are designed to handle ac power.
 
I’m currently charging my battery with generator only so yes it will work.
Growatt 6K inverter
Growatt 5KWH battery
 
One problem is that your growatt is designed for nearly twice the amperage than what the eco flow can provide. I would suggest that to get it working you connect it to grid power at the amperage specification listed in the manual and then experiment with the settings till you find what is causing the unexpected power consumption. Remember an AIO only passes through ac power it doesn’t subsidize it so without a battery you will be either running completely off of the solar or completely off of the ac. I suspect that in order for the inverter to work “directly” from solar it must have some sort of a capacitor involved that may be overwhelming your eco flow. If there is a setting that prevents this you will still have to factor in the power consumption of the growatt itself when it switches to ac. The reason I was questioning what you are trying to accomplish is that I was wondering if it is even technically possible to do what you want with an AIO because of how they are designed to handle ac power.
I Growatt manual "Line Mode Specification" table says:
- Nominal Input Voltage : 230Vac
- Nominal Input Frequency : 50Hz/60Hz
It does not say anything about Nominal Input Current. When you say "growatt is designed for nearly twice the amperage than what the eco flow can provide." it means Nominal Input Current should actually be ~30A.

"I would suggest that to get it working you connect it to grid power" ... connect what to the grid ? The Ecoflow or the Growatt ?

"an AIO only passes through ac power it doesn’t subsidize it so without a battery you will be either running completely off of the solar or completely off of the ac." I don't agree with this statement for my setup : Ecoflow AC-Out connected to Growat AC-in
My setup is working with appliances consuming less than 1KW.
For example: with a toaster consuming 800W, Growatt is taking 300W from solar and 500W from Ecoflow

But it's not working with appliances consuming 1/1.5/2KW because Ecoflow gets overloaded by Growatt.
It might be the case that Growatt demands more than 16A from Ecoflow (overloading it) when it needs to deliver above 1KW to appliances.
If this is the case then conclusions are : the setup is working only with consumers below 1KW.
 
Last edited:
I Growatt manual "Line Mode Specification" table says:
- Nominal Input Voltage : 230Vac
- Nominal Input Frequency : 50Hz/60Hz
It does not say anything about Nominal Input Current. When you say "growatt is designed for nearly twice the amperage than what the eco flow can provide." it means Nominal Input Current should actually be ~30A.

"I would suggest that to get it working you connect it to grid power" ... connect what to the grid ? The Ecoflow or the Growatt ?

"an AIO only passes through ac power it doesn’t subsidize it so without a battery you will be either running completely off of the solar or completely off of the ac." I don't agree with this statement for my setup : Ecoflow AC-Out connected to Growat AC-in
My setup is working with appliances consuming less than 1KW.
For example: with a toaster consuming 800W, Growatt is taking 300W from solar and 500W from Ecoflow

But it's not working with appliances consuming 1/1.5/2KW because Ecoflow gets overloaded by Growatt.
It might be the case that Growatt demands more than 16A from Ecoflow (overloading it) when it needs to deliver above 1KW to appliances.
If this is the case then conclusions are : the setup is working only with consumers below 1KW.
If the new AIO units that can use solar independently of battery can subsidize ac with solar that is awesome ( I wanna get me one) however obviously something isn’t working That straightforward or else you’re idea would work flawlessly. so In order to see how much power your growatt is actually using (use a clamp meter or a shunt not the Growatt display or the eco flow display) you need to have it connected to actual grid power or a generator that can supply enough power to trip the recommend size breaker that feeds your growatt. Then you can see it’s actual amperage use and wattage consumption ( by mutiplying the amps used by the voltage) there might be a setting that will eliminate the sudden inrush of current over a certain wattage. You should expect to see at least a 50 watt loss of power between the wattage into the growatt and the wattage out of the growatt probably more. It would be good before getting to frustrated with the growatt to make sure it actually works if it is setup inside of the parameters it was designed for. It is possible something is wrong with your growatt. I would want to rule that out first.
 
Anyone ever experience issues with an MPP 12v AIO and the predator 3500? I'm trying to help a friend that just left to live in a camper troubleshoot. It charged fine on grid power but they just plugged it into the generator for the first time and all they get is the display flashing and beeping with no fault codes.

I've run through all of the basic t/s ideas I have and I can't find anything in the manual that matches what she's seeing.

The only thing I'm left with is that there's a quirk with the generator that the AIO doesn't like but I can't figure out what it would be.

The AIO is a MPP model PIP - 1012LV-MS
 
Anyone ever experience issues with an MPP 12v AIO and the predator 3500? I'm trying to help a friend that just left to live in a camper troubleshoot. It charged fine on grid power but they just plugged it into the generator for the first time and all they get is the display flashing and beeping with no fault codes.

I've run through all of the basic t/s ideas I have and I can't find anything in the manual that matches what she's seeing.

The only thing I'm left with is that there's a quirk with the generator that the AIO doesn't like but I can't figure out what it would be.

The AIO is a MPP model PIP - 1012LV-MS
Ideas-
-120 or 240v from generator?
 
Ideas-
-120 or 240v from generator?
120v

Today hopefully they'll be able to charge the battery some using a portable solar panel and a victron charge controller. The only thing left they can think of is that the battery is too dead to charge on the AIO.
 
120v

Today hopefully they'll be able to charge the battery some using a portable solar panel and a victron charge controller. The only thing left they can think of is that the battery is too dead to charge on the AIO.
What’s the battery voltage at?
Does your system have a low dc cut off feature?
 
There is no reason for an inverter generator to not work with the Growatt and you will not need a separate charger. Some say we should not plug a charger while it's connected to the Growatt but I did a few times to charge faster and had no issues so far.
I think the only issue would be as the charger raises the voltage to charge the batteries the inverter might throttle down any solar charging from its end, as long as its dc going in to the inverters battery input at suitable voltages the inverter will just use it. I ran my spf3500es off an ebike charger to see if it worked as i didn't have any batteries or pv.
 
Anyone ever experience issues with an MPP 12v AIO and the predator 3500? I'm trying to help a friend that just left to live in a camper troubleshoot. It charged fine on grid power but they just plugged it into the generator for the first time and all they get is the display flashing and beeping with no fault codes.

I've run through all of the basic t/s ideas I have and I can't find anything in the manual that matches what she's seeing.

The only thing I'm left with is that there's a quirk with the generator that the AIO doesn't like but I can't figure out what it would be.

The AIO is a MPP model PIP - 1012LV-MS
I came looking for answers as i tried my diesel genny (non inverter) with my growatt today, it connected and charged for a minute but then just cycles grid bypass/inverter mode.
Looking at the previous comments it seems in my situation it might be frequency locking issue on the inverter (might be your issue too). I will try my petrol inverter genny and see how that goes. I will also try turning off the growatt and see if it will work with the diesel to charge the batteries.
failing that i will source a beefy 48v charger as i specifically want to use the diesel because it can sit for years on standby providing the start battey stays good. I'll be back with results in a few days.

edit: Update: My petrol inverter generator worked perfectly, even triggered bms charge overcurrent protection. I found a 48v 30A charger on ebay for $500 here, and a 45A one for $785 here not sure about its longevity being run on a non inverter generator.
 
Last edited:
Many diesel generators operate at 1800 rpm for 60 Hz or 1500 rpm for 50 Hz.

A lower rpm engine is a bit tougher for governor to tightly control the rpm speed to keep frequency output of generator stable.

Diesel engines usually have a larger flywheel mass to help, but larger mass flywheel also slows the reaction time to compensate for electrical loading on generator.

--------
If you run a separate charger on a generator you should be aware of charger's AC load power factor. Many chargers do not have great AC power factor due to their simple AC to DC rectification and DC filter capacitor. They draw large AC current peaks only at the sinewave voltage peaks (high current crest factor). This means heavier peak load current for average output power on generator so you will not be able to get full power output rating capability from generator.
 
Last edited: