lotsofyoda
New Member
- Joined
- Sep 19, 2022
- Messages
- 8
I bought my equipment from Signature Solar (SS).
6 x Growatt 5000 es in parallel
18 x EG4 5.1kwh 48v batteries (92kwh)
96 solar panels with nearly 38kw
All working fine.
I’m 100% off grid. No utility backup. Large 6000 sft home in Idaho.
My system is sized large on purpose to allow charging of my electric vehicle (Hyundai Ioniq 5) and running some other heavy loads even in winter - off grid. I’m not afraid to add more panels or more battery if needed in the future.
Batteries are all Using their own BMS, meaning they’re not connected to the inverters to communicate/be managed by the inverters.
I have 6 batteries to a rack with bus bars. Each of the 3 racks connect to a massive bus bar which is my battery bank terminal. My 6 inverters each connect and draw from this massive terminal bus bar.
Here’s my problem/challenge.
The inverters (paralleled and communicating with each other) can manage only 16 batteries through the inverter BMS. The EG4 batteries only have dip switches for 16. I think that’s part of the limitation.
I have 18 batteries in the bank. So I can’t use the inverter BMS. (SS recommended to let all the batteries manage themselves through their own BMS)
I would prefer to keep my 18 batteries (or expand larger even over time) in my bank.
My inverters don’t know and can’t report battery bank SOC. I’m trying to configure that my generator (Cummins 20kw propane) starts up when battery bank goes down to 15% as a backup option.
What are my options?
(1) stay as is. Let each battery manage itself. Get an external device to fire my generator.
(2) disconnect 2 batteries to get to 16 and let inverter manage bank and generator.
(3) let inverters manage 16 batteries and keep additional 2 batteries in bank, managing themselves with own BMS
(Problematic?)
(4) add some other tool/gizmo to manage my system?
(5) some Other solution I can’t even imagine because I don’t know what I don’t know.
6 x Growatt 5000 es in parallel
18 x EG4 5.1kwh 48v batteries (92kwh)
96 solar panels with nearly 38kw
All working fine.
I’m 100% off grid. No utility backup. Large 6000 sft home in Idaho.
My system is sized large on purpose to allow charging of my electric vehicle (Hyundai Ioniq 5) and running some other heavy loads even in winter - off grid. I’m not afraid to add more panels or more battery if needed in the future.
Batteries are all Using their own BMS, meaning they’re not connected to the inverters to communicate/be managed by the inverters.
I have 6 batteries to a rack with bus bars. Each of the 3 racks connect to a massive bus bar which is my battery bank terminal. My 6 inverters each connect and draw from this massive terminal bus bar.
Here’s my problem/challenge.
The inverters (paralleled and communicating with each other) can manage only 16 batteries through the inverter BMS. The EG4 batteries only have dip switches for 16. I think that’s part of the limitation.
I have 18 batteries in the bank. So I can’t use the inverter BMS. (SS recommended to let all the batteries manage themselves through their own BMS)
I would prefer to keep my 18 batteries (or expand larger even over time) in my bank.
My inverters don’t know and can’t report battery bank SOC. I’m trying to configure that my generator (Cummins 20kw propane) starts up when battery bank goes down to 15% as a backup option.
What are my options?
(1) stay as is. Let each battery manage itself. Get an external device to fire my generator.
(2) disconnect 2 batteries to get to 16 and let inverter manage bank and generator.
(3) let inverters manage 16 batteries and keep additional 2 batteries in bank, managing themselves with own BMS
(Problematic?)
(4) add some other tool/gizmo to manage my system?
(5) some Other solution I can’t even imagine because I don’t know what I don’t know.