Do parallel batteries increase continuous discharge rate? Connector upgrade required?

Patel

New Member
Joined
Oct 6, 2022
Messages
30
Hello,

I am thinking about buying a battery, it is 48v and max continuous discharge current of 150 amps.

My question is, if I parallel 2 of these batteries, does it increase the max continuous discharge current to 300 amps?

Also, the stock connector which is included with the battery is the Anderson 150 amp connector, if I am paralleling 2 of these batteries, do I need to use the Anderson 350 cable to connect to the inverter and between the batteries?

Thank you very much
 
You need the Anderson 150 from battery 1 to a buss or inverter terminal and another 150 from battery 2 to the buss or inverter terminal (keep wire lengths the same).
 
Hello,

I am thinking about buying a battery, it is 48v and max continuous discharge current of 150 amps.

My question is, if I parallel 2 of these batteries, does it increase the max continuous discharge current to 300 amps?

Also, the stock connector which is included with the battery is the Anderson 150 amp connector, if I am paralleling 2 of these batteries, do I need to use the Anderson 350 cable to connect to the inverter and between the batteries?

Thank you very much
Yes.
As long as the overall cabling supports the increased amperage.
 
And you typically would not want to max out the allowable discharge rate so if you truly need 300A it would be better to have 3 so you are theoretically only pulling maximum of 100A per battery.
 
If you’re going to use those, please check the specs for voltage. If its a 48 volt system, I’d want the connector rated for 60 volts.

I use Anderson plugs for solar panel hookup and I have difficulty finding the voltage rating for the ones I use. It’s in excess of 100 volts for mine, and I don’t exceed 66 volts. Anderson does make a 150 amp connector that is only rated for 36 volts.
 

Is that true if 4 batteries of 100 ah linked as parallel will b 400 ah bcz parallel will increase amps not voltage but when i discharge or charge it s still 100 ah each or i can calxulate as 400 ah in discharge or charge bcz 400 as capacity differ from 100
 
Your system with 4 100Ah batteries in parallel can be treated as a single 400Ah battery. Your charge/discharge currents will split evenly between each battery, so if you are pulling 200A for the inverter, each battery BMS only passes 50A. The trick here is to stay away from the top or bottom. If you were pulling the 200A and two batteries cut out for low voltage disconnect, the remaining two pick up the load and now would be passing 100A each. When one of those two cuts out the BMS will have an overcurrent trip.
 
O
Your system with 4 100Ah batteries in parallel can be treated as a single 400Ah battery. Your charge/discharge currents will split evenly between each battery, so if you are pulling 200A for the inverter, each battery BMS only passes 50A. The trick here is to stay away from the top or bottom. If you were pulling the 200A and two batteries cut out for low voltage disconnect, the remaining two pick up the load and now would be passing 100A each. When one of those two cuts out the BMS will have an overcurrent trip.
k so what do you advise put max discharge and max charge for such 400 ah rack ?
 
so what do you advise put max discharge and max charge for such 400 ah rack ?

Each BMS has its over current settings. My 150A JBD BMS is set for 160A for 10 seconds (factory default). Those limits protect the BMS and no need to alter them. In my 400A bank example, if each BMS can handle 100A, in theory the bank can handle 400A of charge or discharge.

In my real life system, I have 3 280Ah 12V batteries in parallel to a 2000W inverter. On the charging side PDI9160L converter and an Epever SCC at 40A. I get nowhere near any of the limits for my equipment and one battery can pretty much serve the loads.

In a big bank, the wires from each battery need to be sized/fused for the BMS limit (100A) to the buss bar. From the buss bar to the inverter needs to be sized for the total of the 4 batteries, thus 400A rated wire.
 
I would say technically yes, but you I would down rate by 20% ... batteries could be not 100% balance and not perfectly even
 
so what do you advise put max discharge and max charge for such 400 ah rack ?

Each BMS has its over current settings. My 150A JBD BMS is set for 160A for 10 seconds (factory default). Those limits protect the BMS and no need to alter them. In my 400A bank example, if each BMS can handle 100A, in theory the bank can handle 400A of charge or discharge.

In my real life system, I have 3 280Ah 12V batteries in parallel to a 2000W inverter. On the charging side PDI9160L converter and an Epever SCC at 40A. I get nowhere near any of the limits for my equipment and one battery can pretty much serve the loads.

In a big bank, the wires from each battery need to be sized/fused for the BMS limit (100A) to the buss bar. From the buss bar to the inverter needs to be sized for the total of the 4 batteries, thus 400A rated wire.
On the catalogue it mentioned if 400 ah u can go 0-120 A as charge or discharge but im asking as long your more experiences than me
 
so what do you advise put max discharge and max charge for such 400 ah rack ?

Each BMS has its over current settings. My 150A JBD BMS is set for 160A for 10 seconds (factory default). Those limits protect the BMS and no need to alter them. In my 400A bank example, if each BMS can handle 100A, in theory the bank can handle 400A of charge or discharge.

In my real life system, I have 3 280Ah 12V batteries in parallel to a 2000W inverter. On the charging side PDI9160L converter and an Epever SCC at 40A. I get nowhere near any of the limits for my equipment and one battery can pretty much serve the loads.

In a big bank, the wires from each battery need to be sized/fused for the BMS limit (100A) to the buss bar. From the buss bar to the inverter needs to be sized for the total of the 4 batteries, thus 400A rated wire.
On the catalogue it mentioned if 400 ah u can go 0-120 A as charge or discharge but im asking as long your more
And you typically would not want to max out the allowable discharge rate so if you truly need 300A it would be better to have 3 so you are theoretically only pulling maximum of 100A per battery.
i have 4 in parallel total 400 ah u think i can put 100 charge and discharge ?
 
i have 4 in parallel total 400 ah u think i can put 100 charge and discharge ?

100A charge/discharge would be well within the limits. That works out to 25A per battery.
 