Sol-Ark 15k Load/Grid 0W after changing to "Limited to Home" setting

MuckMuck

New Member
Joined
Oct 31, 2022
Messages
4
Has anyone else seen this and know how to resolve it? After changing the work mode from Grid sell to "Limited to home", and changed some TOU settings, all of the sensor values for bat/load/grid are almost 0 watts. The only value registering is the 500w of battery being fed to the house. The remaining 12k watts feeding the load is not registering. Verified the 12k watts at the main breaker panel but Sol-ark reporting just the 500 watts TOU. SA_CTissue.jpg
 
Never mind. I didn't think the CT sensors were required in my configuration but they are apparently. Installed CT and ran the auto detect and things look correct now.
 
@MuckMuck are you setup like this? And the CTs were required? They don't have the CTs on this drawing, but they do in others, so I was unsure if they are needed or not.

SolArk-Standard.jpg

This drawing DOES show the CTs..