Megarevo RxLNA Discussion

3 x 16s EVE LF280K. I'm not sure of the true usable capacity, maybe 40kWh? (I just figured out I can make a signature) :)
 
Last edited:
Also does anyone know how you can adjust the upper low 120 voltage range. The grid voltage is 131 or 133v sometimes without exporting and that triggers overvoltage alarms and switches to battery. I simply want to increase that range to 140v. You can only adjust the 220v range from what I've seen
 
Also does anyone know how you can adjust the upper low 120 voltage range. The grid voltage is 131 or 133v sometimes without exporting and that triggers overvoltage alarms and switches to battery. I simply want to increase that range to 140v. You can only adjust the 220v range from what I've seen
If your grid has that high voltage, you should contact your utility company.
There should be a transformer close to your home where they could adjust the ratio between input/output.
The nominal voltage should be 120 volt per split phase so 240 volt together. Your 2 x 133 = 266 volt.
That is almost 11% over the nominal voltage.

I found this document with some searching:
Basically, the Range A service voltage range is plus or minus 5% of nominal.
The Range B utilization voltage range is plus 6% to minus 13% of nominal.

So it seems your 11% is way out of line.
Hence my suggestion to contact your utility company.
Not something you should adjust on your inverter IMO.

*UPDATE*
I just saw your location is not the USA so your local conditions might be different. Check with your local utility.
 
Last edited:
I installed this firmware today to test it. I guess it's from 2023.
Also attached is another manual from Megarevo.

The Tool is in English now and there is a new setting "Home Load" my guessing is refering to the Main Panel, but new manual doesn't mention it.
You need to decompress the file two times, the second one is the Tool now called hybrid in EN.
If you select Grid Set 220V, you can see Home Load on the screen, but if you use 120/240, Homeload will disappear from the screen, from what I noticed.

Really not sure what option to use if Grid Set 220V or 120/240


Firmware
ARM: V1.03.06
DSP: V1. 00. 06
200100 000000
 

Attachments

  • firmware.zip
    11.1 MB · Views: 58
  • LNA series hybrid inverter user manual V1.4.pdf
    4.4 MB · Views: 77
I installed this firmware today to test it. I guess it's from 2023.
Also attached is another manual from Megarevo.

The Tool is in English now and there is a new setting "Home Load" my guessing is refering to the Main Panel, but new manual doesn't mention it.
You need to decompress the file two times, the second one is the Tool now called hybrid in EN.
If you select Grid Set 220V, you can see Home Load on the screen, but if you use 120/240, Homeload will disappear from the screen, from what I noticed.

Really not sure what option to use if Grid Set 220V or 120/240


Firmware
ARM: V1.03.06
DSP: V1. 00. 06
200100 000000
The firmware I posted on this link
has the same MD5 checksum for .out file

Your version:
md5sum DSP/HybridInverter8KSNA_v1.4.13.B03D06.out
c643e7ec2e5732a5de17fca378a992b4 DSP/HybridInverter8KSNA_v1.4.13.B03D06.out

vs mine:
md5sum HybridInverter8KSNA_v1.4.13.B03D06_20221210.out
c643e7ec2e5732a5de17fca378a992b4 HybridInverter8KSNA_v1.4.13.B03D06_20221210.out


So the other file is newer:
hybrid_app8K_V19_2.axf
vs
hybrid_app_8K_V20.axf

Homeload is indeed a new thing it seems:

On V19:
strings hybrid_app8K_V19_2.axf | grep -i homeload -> yields nothing

where as on V20
strings ARM/hybrid_app_8K_V20.axf |grep -i homeload -> show 40 occurrences

Regarding manual:
The manual pdf is labeled v1.4 but the first page shows v1.3
On page 4 it shows there is now also a 10kW version: R10KLNA.
I had seen that model mentioned in the spec sheets, not in the manual so far.

I learned something new today. I had asked MR support rep about powering a RSD device, and basically got no answer.
In this manual it clearly shows how to hook it up on page 31(labeled 30).

If you don't mind me asking:
How did you get a hold of the new firmware/manual ?
 
The firmware I posted on this link
has the same MD5 checksum for .out file

Your version:
md5sum DSP/HybridInverter8KSNA_v1.4.13.B03D06.out
c643e7ec2e5732a5de17fca378a992b4 DSP/HybridInverter8KSNA_v1.4.13.B03D06.out

vs mine:
md5sum HybridInverter8KSNA_v1.4.13.B03D06_20221210.out
c643e7ec2e5732a5de17fca378a992b4 HybridInverter8KSNA_v1.4.13.B03D06_20221210.out


So the other file is newer:
hybrid_app8K_V19_2.axf
vs
hybrid_app_8K_V20.axf

Homeload is indeed a new thing it seems:

On V19:
strings hybrid_app8K_V19_2.axf | grep -i homeload -> yields nothing

where as on V20
strings ARM/hybrid_app_8K_V20.axf |grep -i homeload -> show 40 occurrences

Regarding manual:
The manual pdf is labeled v1.4 but the first page shows v1.3
On page 4 it shows there is now also a 10kW version: R10KLNA.
I had seen that model mentioned in the spec sheets, not in the manual so far.

I learned something new today. I had asked MR support rep about powering a RSD device, and basically got no answer.
In this manual it clearly shows how to hook it up on page 31(labeled 30).

If you don't mind me asking:
How did you get a hold of the new firmware/manual

I just sent a message to Megarevo Support WhatsApp number. We had a conversation and I sent everything they ask me and at the end they sent me the firmware and manual. They were probably in a good mood.
 
The manual mention an Advance Setting that is not in that firmware yet
Hahahaha... that is exactly what I just found out after flashing the new firmware and I was just going to write about it ;-)

Screenshot from 2023-01-29 16-06-05.png
Arm and DSP stayed the same, only left of bottom line went from 190100 to 200100.
I don't see any further changes.
This version does have the generator setup included btw:
Screenshot from 2023-01-29 16-08-22.png
 
Hahahaha... that is exactly what I just found out after flashing the new firmware and I was just going to write about it ;-)

View attachment 132138
Arm and DSP stayed the same, only left of bottom line went from 190100 to 200100.
I don't see any further changes.
This version does have the generator setup included btw:
View attachment 132139

I noticed the grid is not feeding now the 200-300w supplementing the battery.
 
Does anyone have existing grid tie PV inverters in use with these inverters? The manual has zero mention of AC coupling. The inverters seem to be pretty nice, with the exception of the firmware/software which is typical of the imported inverters.

I have a need to add batteries to existing grid tied systems. The only solutions that appear solid/trouble free are outback/schneider for my AC coupled usage due to KW in/out required. I am drawn to these inverters due to larger KW output on the larger models. I have a project with 3 x 6.0KW SMA GT's and wanted to try and reuse the GT's, but appears that rewiring to DC coupling would be the only solution with the Megarevo's. Even with other solutions I planned on rewiring 1 or 2 GT's and trying to keep a mix of both DC and AC Coupling.
 
Last edited:
If your grid has that high voltage, you should contact your utility company.
There should be a transformer close to your home where they could adjust the ratio between input/output.
The nominal voltage should be 120 volt per split phase so 240 volt together. Your 2 x 133 = 266 volt.
That is almost 11% over the nominal voltage.

I found this document with some searching:


So it seems your 11% is way out of line.
Hence my suggestion to contact your utility company.
Not something you should adjust on your inverter IMO.

*UPDATE*
I just saw your location is not the USA so your local conditions might be different. Check with your local utility.
L-L voltage is not 266 but in this case 223 or something. The location has a 2phase 2x127/220v supply (2 phases out of 3)
At this moment both legs are 130v, didnt trigger overvoltage yet.
 

Attachments

  • Screenshot_20230130_071104_SOLARMAN Business.jpg
    Screenshot_20230130_071104_SOLARMAN Business.jpg
    154.8 KB · Views: 15
I re-read your sentence multiple times but I have a hard time understanding what you are trying to say.
Could you elaborate a bit please ? (non-native english speaker here)

I re-read your sentence multiple times but I have a hard time understanding what you are trying to say.
Could you elaborate a bit please ? (non-native english speaker here)

We are two non native english speaker and mine probably is worst lol.

I can export because I have Net Metering.

My inverter most of the time supply 200-300w from the grid constantly even when my battery was charged in the night or my production was high enough to charge the battery and supply the Loads.

Now is not doing that. The inverter is using the battery and production to supply the loads and there is nothing from the grid.

One of the pictures show 200w from the grid even my production was high and the second one with the firmware update is not doing that.
 

Attachments

  • 0A71DB25-28AF-401E-8D43-556E9A28F148.png
    0A71DB25-28AF-401E-8D43-556E9A28F148.png
    445.1 KB · Views: 21
  • 23AC1135-8CC9-4265-862D-60AD40D4C43E.png
    23AC1135-8CC9-4265-862D-60AD40D4C43E.png
    496.1 KB · Views: 21
My inverter most of the time supply 200-300w from the grid constantly even when my battery was charged in the night or my production was high enough to charge the battery and supply the Loads.

Now is not doing that. The inverter is using the battery and production to supply the loads and there is nothing from the grid.

One of the pictures show 200w from the grid even my production was high and the second one with the firmware update is not doing that.
I am running the latest software.
I still see what you are describing.
This is a graph from my smart meter, so real power from/to grid over the last hour after sun set:
Screenshot from 2023-01-30 19-54-25.png
about 5 minute intervals, still 420 watt into the grid.

When I look at my sense unit where I can see per phase, i see this:


Screenshot_crop.png
one of the phases is pulling power, the other is putting energy in the grid (from the battery)

Not Good [TM]
 
I am running the latest software.
I still see what you are describing.
This is a graph from my smart meter, so real power from/to grid over the last hour after sun set:
View attachment 132366
about 5 minute intervals, still 420 watt into the grid.

When I look at my sense unit where I can see per phase, i see this:


View attachment 132367
one of the phases is pulling power, the other is putting energy in the grid (from the battery)

Not Good [TM]
Damn, I hope the next version with advanced settings will solve that.
 
Last edited:
A reboot should clear the error in the interim, but you'll have to know the loads to predict why its happening. Are you using the solarman wifi adapter? Can you share the consumption graphs?
 
Is anyone able to Remote Control their inverter thru solarman Pro/Business interface? I see you can set peak shift times and toggle EPS, etc thru the Home solarman interface, but it says not available when I try to access thru Pro. Is this a limitation of these other interfaces?
 
Is anyone able to Remote Control their inverter thru solarman Pro/Business interface? I see you can set peak shift times and toggle EPS, etc thru the Home solarman interface, but it says not available when I try to access thru Pro. Is this a limitation of these other interfaces?
I am not sure you can but the dongle does have the ability to do that. Which is what I was kinda worrisome for me, having a device ran off a server in China with the ability to control the power at my house. This is one of the many reasons I got rid of the wifi dongle and only went with modbus serial connection on a local device.
 
Its a bummer because I like the pro interface better, but home seems to give more options. As far as the Chinese companies, you can either delete them from the dongle or thru solarman interface. Although I'm not sure if that completely locks out their access.
 
Its a bummer because I like the pro interface better, but home seems to give more options. As far as the Chinese companies, you can either delete them from the dongle or thru solarman interface. Although I'm not sure if that completely locks out their access.
I have found, like most iot Chinese things, they always put a back door in there for data gathering.
 
For those of you who have one would you buy it again? And is the blue sun BSE-8KLNA the same inverter ( can use megarevo updates). I got bit by the LVX6048 and looking for a replacement
 