Can you post what each MPPT is receiving and producing?I have a big update on this.
I have been successul in getting 18Kw now from my array. The way I did that was sending about 10kw in to my batteries. There is a limit on actual inverting output power on the Solark15k of about 15kw (makes sense). That said - The limit of DC PV going direct to battery in combination with inversion is 18kw - PERIOD I've not seen it do 19.2 as stated in manual. That 18kw is a limitation in the software that if you change it, it just reverts back, even in powerview.
Solark did tell me they are working on a fix for the limiting power. Interesting enough, they seem focused on the MPPT limiting amerage, which I was as well for a while. I feel silly that I never discharged my batteries far enough to prove this out until now. It seems so simple now, and Solark should have stated this more clearly in their marketing.
They had me thinking I have an a line voltage issue, while my microinverters have ZERO issues. They do not disconnect and they are UL1741SA just like the Solark.
Oh well, It sounds like this is what it is, unless we get some software update that changes things. Good news is, they have admitted the issue and I am talking to a new person on the Solark side that seems to understand and is honest about "their" issue. So I guess, this is may be a hopeful start to a real solution.
TLDR: - Solark 15k will produce 18kw max DC-PV to DC and will only allow a total inversion of 15kw when you add the load and the grid sell numbers together it will always = 15kw. I had never caught on to that until I had an epiphany the other day. ???????
The load + the Grid will NEVER be over 15kw. I believe that is the end of the story.
View attachment 134999
View attachment 135000
That panel sizing calculator Sol-Ark has on their website always maxes out at 6500W (6440?) per MPPT. However, someone here posted over 7200W on a MPPT making power.