Is that your G99 application. I have one in at the moment since begining of July and heard nothing. Wondering if I should go ahead and install and send in the commissioning sheets A3-2 and G100.
After the G99 fast track application you should receive a confirmation that they have accepted the application so you can then install & what export they would allow. In my case the DNO said I fell under SGI-3 which is up to 32A export.
 
After the G99 fast track application you should receive a confirmation that they have accepted the application so you can then install & what export they would allow. In my case the DNO said I fell under SGI-3 which is up to 32A export.
Will hold fire and see if anything comes back in the next two weeks then send an email to let them know I am still alive.
 
Today Sofar tech support have updated the inverter remotely to v3.32.
After testing this seems to have cured the issue.
When grid CT is disconnected an ID35 error is generated & the Inverter shuts down.
Upon reconnection the unit does it's 60s countdown before resuming operation.
Now complies with G100.
 
Last edited:
Hi All, maybe someone can advise. I applied for and got consent from my DNO ( UK POWER NETWORKS ), to install a Sofar ME3000 SP with lead acid batts. I already have 4kw pv panels. Of course the ME3000 SP is a 3kw unit. I notice in the "Commissioning Data " section in my account on the DNO website, they will want me to confirm G99 compliance, I suspect this is because the solar panels at 4kw plus the ME3000SP at 3kw would equal a possible 7KW export to grid. They also ask for forms A2-1 and A2-2 to be completed, these forms I think are to show the mE3000SP is G99 compliant, but if I understand correctly the ME3000 SP is only G98 and G100 compliant. They say the ME3000SP failed the ELIGABILITY TEST ", yet the ME3000SP does appear in the ENA register . If I do need to provide forms A2-1 and A2-2 can I get these from somewhere ready completed. Any help or thoughts greatly appreciated.
 

Attachments

  • 2023-10-29 08_40_59-Commissioning Data Page 2 of 2 - Commission Data - 2 - Low Carbon Applicat...png
    2023-10-29 08_40_59-Commissioning Data Page 2 of 2 - Commission Data - 2 - Low Carbon Applicat...png
    41.7 KB · Views: 3
Hi All, maybe someone can advise. I applied for and got consent from my DNO ( UK POWER NETWORKS ), to install a Sofar ME3000 SP with lead acid batts. ...
...
They say the ME3000SP failed the ELIGABILITY TEST ", yet the ME3000SP does appear in the ENA register . If I do need to provide forms A2-1 and A2-2 can I get these from somewhere ready completed. Any help or thoughts greatly appreciated.
Can you clarify ? The two bits in bold seem to contradict each other?
 