Highly unlikely the generator will be stable enough to satisfy the GT inverter requirements. When on generator, the SolArk is slave to generator freq/phase.
When on generator or grid input, the SolArk is not allowed to do freq shifting power control on GT inverter power output.
You could put a disconnect relay on GT feed to remove GT inverter when generator start is attempted.
When on generator or grid input, the SolArk is not allowed to do freq shifting power control on GT inverter power output.
You could put a disconnect relay on GT feed to remove GT inverter when generator start is attempted.