Sanity Check

whlla

New Member
Joined
Jun 1, 2020
Messages
4
Brand new to this and I've been staring at wire sizing charts for a couple days now bouncing around different ideas.
How does this look for starting layout?

untitled (1).png

Buddy had some 2/0 gauge wire laying around so figured I could use that for green wires in diagram. The charge controller however has max of 6 gauge for its terminals. Would it be alright to use 6 gauge on the red wires in diagram? Anything else out of place or wrong that I should correct? Not trying to burn the house down
 
I don't trust breakers over 200 amps.
I suggest you add an mrbf fuse of 250 amps at the battery positive and a disconnect switch between the fuse and the positive busbar.
The inverter positive wire should be fused at 250 amps.
Suggest a shunt between the battery negative terminal and the negative busbar.
A 100 amp hour lifepo4 battery can't supply enough current for that inverter.
 
A 100 amp hour lifepo4 battery can't supply enough current for that inverter.
I was just typing the same, plus no info on panel size or voltage. Not sure 2/0 wire size is good enough either.

OP do you really need a 2.2kW inverter ? or intend to ever run it at full capacity ?
 
I was just typing the same, plus no info on panel size or voltage. Not sure 2/0 wire size is good enough either.

OP do you really need a 2.2kW inverter ? or intend to ever run it at full capacity ?
2/0 awg is fine unless the wires are unexpectedly long but the high current fuses should be 275 amps.
 
Thank you guys for your help.

No intention of using full capacity, I only plan on using about 200-500 watts for now (fridge and lights) until I can afford another battery.
Yeah realizing inverter is large and thinking about returning and getting something in 1000-1500 range. Wanted to get an inverter I could continue to use as I increased load + batteries.

I had been using this table for sizing breakers, but if I should avoid breakers over 200A then will need to change to fuses.
Panels wise I was thinking of two of these in series (310w, 40.0V voc, 9.83A isc).

So 250/275 amp fuses on battery and inverter positive, remove the 250 amp breaker on battery and add disconnect switch, and consider downsizing inverter?
 
Thank you guys for your help.

No intention of using full capacity, I only plan on using about 200-500 watts for now (fridge and lights) until I can afford another battery.
Yeah realizing inverter is large and thinking about returning and getting something in 1000-1500 range. Wanted to get an inverter I could continue to use as I increased load + batteries.

I had been using this table for sizing breakers, but if I should avoid breakers over 200A then will need to change to fuses.
Panels wise I was thinking of two of these in series (310w, 40.0V voc, 9.83A isc).

So 250/275 amp fuses on battery and inverter positive, remove the 250 amp breaker on battery and add disconnect switch, and consider downsizing inverter?

Yep.
If you are a bit careful I say keep the inverter.
Maybe put a 15 amp fuse on the ac side.
 
Now I might be wrong here, but the breaker rating was calculated at inverter full use.
If your only going to use 500W or there about's, then then the fuse/breaker can be much less on the low side. Understand though it will break/blow if you forget and connect a bigger load to the higher voltage inverter side.

You could stick a breaker on the high voltage side of the inverter in like a small CU. Then you can protect the low voltage side with a good quality 200A breaker, and then use it as a disconnect - whilst protecting against an overload situation like short in the inverter or cable.

Thats what I have done, I am well oversized with my inverter - but never intend to use it to the full capacity.
 
Heres how I calculate the wire and fuse for the inverter.
2200 ac watts / .85 conversion efficiency / 12 volts = 215.68627451 dc amps
215 dc amps * 1.25 fuse factor = 269.607843137 fusible amps.
 
On second though, maybe you should put a 125 amp mrbf fuse on the postitive terminal and swap for the 275 amp fuse when you add a 2nd battery.
 
On second though, maybe you should put a 125 amp mrbf fuse on the postitive terminal and swap for the 275 amp fuse when you add a 2nd battery.
Doesn't the fuse rely on the load ? So no mater how many batteries are connected - its only going to blow if the load is greater than the rated capacity of said fuse ?

I reckon a 100amp cheap Chinese breaker would do it for the 12v side after tails to protect the inverter, with a 150A fuse at the battery terminal to protect the tails against a short. And a 6 amp breaker post inverter would suffice against an overload. AC Voltage of 110 is an assumption here.

What do you think ? @smoothJoey
All input is good.
 
Doesn't the fuse rely on the load ? So no mater how many batteries are connected - its only going to blow if the load is greater than the rated capacity of said fuse ?

I reckon a 100amp cheap Chinese breaker would do it for the 12v side after tails to protect the inverter, with a 150A fuse at the battery terminal to protect the tails against a short. And a 6 amp breaker post inverter would suffice against an overload. AC Voltage of 110 is an assumption here.

What do you think ? @smoothJoey
All input is good.


I can't bring myself to endorse a cheap chinese breaker even if its backed by a proper fuse.
MRBF fuses are ~$10USD from waytech. Buy 2 and learn quickly :)
 
I can't bring myself to endorse a cheap chinese breaker even if its backed by a proper fuse.
MRBF fuses are ~$10USD from waytech. Buy 2 and learn quickly :)
Yeah - fair enough - no cheap Chinese shite, but the logic is sound ?
 
Man, thank you guys so much for your help. I am picking up some mbrf fuses and a good 100A breaker.
 