    Tying in 3 phase Grid power to my XW Pro 6848 Invertes

    Thanks for the the suggestions.
  2. C

    Tying in 3 phase Grid power to my XW Pro 6848 Invertes

    You are correct sir. An insight on my part. Thanks for the heads up.
  3. C

    Tying in 3 phase Grid power to my XW Pro 6848 Invertes

    I assumed from the documentation you referenced that the XW pro 6848 only provides 3 phase in a wye configuration but, it doesn't indicate that 3 phase delta from the grid cannot be fed into the inverters one leg per inverter. I was hoping that this is the case so if the batteries run low the...
  4. C

    Tying in 3 phase Grid power to my XW Pro 6848 Invertes

    I have 3 XW Pro 6848 interters configured to run 3 phase powder from my Battery backs and it works great. I am now trying to ty in the grid power which is 3 phase delta with the high leg. The first inverter qualifies the grid AC but, the other two legs are always stuck in qualifying AC. I...
  5. C

    Schneider XW Pro 6848 Fault code F01

    Thanks. I am currently working with Schneider. Hopefully they have a viable solution.
  6. C

    Schneider XW Pro 6848 Fault code F01

    Yes, I have tried to factory resetting and even reloading the latest firmware. To be honest with you this is the 2nd inverter that has thrown this fault. Schneider and the Vendor honored the warranty on the first one and replaced it but, their engineering support has been less than stellar. I...
  7. C

    Schneider XW Pro 6848 Fault code F01

    Yes, I understand that. The voltage was measured from the neutral to each leg. I also took the inverter that was throwing the fault F01 out of the 3-phase network and reconfigured into single 120 Vac mode and it still throws the fault F01. When it is in 120Vac mode the inverter turns on...
  8. C

    Schneider XW Pro 6848 Fault code F01

    Yes, the output breakers are open with no load. When they first come on line and the inverters are working momentarily it only measures 5.5 Vac and the other two interters are measuring 117 Vac then the F01 fault is thrown and the inversion shuts down in all three inverters.
  9. C

    Schneider XW Pro 6848 Fault Code F01

    Thanks, was not sure I posted in the correct section.
  10. C

    Schneider XW Pro 6848 Fault Code F01

    I have 3 Schneider XW Pro 6848 inverters that I have configured for 3-phase power operation. Currently When powering the system one of the inverters throws a fault code F01 indicating "Low AC output voltage" and then all three inverters stop inverting. Any help in resolving this issue would be...
  11. C

    Schneider XW Pro 6848 Fault code F01

    It is a new install. It worked for a while when connecting a 3-phase motor and running it for a few minutes and then the F01 fault that never goes away.
  12. C

    Schneider XW Pro 6848 Fault code F01

    It is a new install. It worked for a while when connecting a 3-phase motor and running it for a few minutes and then the F01 fault that never goes away.
  13. C

    Schneider XW Pro 6848 Fault code F01

    I have 3 Schneider XW Pro 6848 inverters that I have configured for 3-phase power operation. Currently When powering the system one of the inverters throws a fault code F01 indicating "Low AC output voltage" and then all three inverters stop inverting. Any help in resolving this issue would be...