solarsemi
New Member
Hi All,
First time posting here. I am early in the process of planning a modest 4 kW system for my home in Toronto, Canada. I'm hoping to receive some reassurance on my understanding so far and collect input on what I have not considered so far. I'm hoping to design the system, source most/all of the equipment myself, coordinate some/all of the permitting and work with an electrician for the install.
Here are my notes so far:
Questions:
Thanks in advance
First time posting here. I am early in the process of planning a modest 4 kW system for my home in Toronto, Canada. I'm hoping to receive some reassurance on my understanding so far and collect input on what I have not considered so far. I'm hoping to design the system, source most/all of the equipment myself, coordinate some/all of the permitting and work with an electrician for the install.
Here are my notes so far:
- 100A service to the home. Panel is full. Considering a small sub-panel expansion to make room for a new back-feed breaker.
- I am pre-approved by Toronto Hydro for a 4kW system (I have not submitted the official net metering application, but no red flags after an initial review)
- My understanding is that a 4kW system should generate about 4-4.5 MWh which would meet our current needs
- We have a gas furnace and gas stove. No EV right now
- I have about 250 sqft of flat roof with no obstructions. I haven't selected a specific panel model yet, but after some searching it seems realistic that 250 sqft can support 4kW of panels
- Planning on using a ballasted flat roof mounting system that supports 5-10 degrees of tilt, facing south. I know I'll need a structural engineer's assessment for this
- I have my eye on the Growatt MIN 3800TL-XH-US for the inverter and connecting it load-side
- 3.8kW at 240V will produce 15.8A peak. This is compatible with using a 20A breaker which appears to be allowable by code for 100A service (rule 64-112 4) ...similar to the 120% rule in the US from what I can tell)
- I've read through the ESA bulletins on PV systems, but am not experienced with code rules in general
- 3.8kW at 240V will produce 15.8A peak. This is compatible with using a 20A breaker which appears to be allowable by code for 100A service (rule 64-112 4) ...similar to the 120% rule in the US from what I can tell)
- I am familiar with cold temp voltage derating for when assembling strings
- Longer term, I'd love to install a solar carport in the backyard. I have about 200 sqft back there which could maybe approach another 4kW array if I used bifacial panels.
- No battery storage planned at this time due to space contraints
Questions:
- Can anyone with Canadian electrical code experience comment on key considerations for a single line diagram? I'm a little unsure of what over-current protections are needed in addition to a back fed breaker
- Does anyone have suggestions for installers in the greater Toronto area or tips on Canadian vendors for sourcing equipment?
- Specific flat roof mounting system recommendations?
- Any other inverters out there comparable to the Growatt?
- Any reason to consider a service side interconnect? Load side seems less expensive and less complicated. I suppose the main benefit of service side would be not having to expand the panel.
- What else should I be considering while planning this system with respect to increased electrical loads in the future (heat pump, induction cooktop, EV charger all possible) and the option of being able to support a few more kW on a carport?
Thanks in advance