Hello,

I am about to hook up my two solar arrays

PV Array1 44.3 VOC x 4 = 177.2 volts (In series)

PV Array2 39.9VOC x 10 = 399 volts (In series)

I called signature solar and they said each mppt can take 500 volts.
I see this in the spec sheet: Max PV Array Open Circuit 500VDC
I just want to confirm this.

Thank you in advance!
 
Hello,

I am about to hook up my two solar arrays

PV Array1 44.3 VOC x 4 = 177.2 volts (In series)

PV Array2 39.9VOC x 10 = 399 volts (In series)

I called signature solar and they said each mppt can take 500 volts.
I see this in the spec sheet: Max PV Array Open Circuit 500VDC
I just want to confirm this.

Thank you in advance!
That is correct, 500V max PV input for EACH MPPT. BTW, the VOC will go up as the temperature goes down so I usually factor in 15% less than max PV input Voltage just to be safe.
You were lucky that you talked to the right person at SS, not like the one below:
 
That is correct, 500V max PV input for EACH MPPT. BTW, the VOC will go up as the temperature goes down so I usually factor in 15% less than max PV input Voltage just to be safe.
You were lucky that you talked to the right person at SS, not like the one below:
Thank you Bud!

This is a huge relief.
 