Home active load greater than Rated AC Input/Output for Deye hybrid SG04LP3.

dmtr_user

New Member
Joined
Feb 1, 2024
Messages
5
Location
Black Sea cost
Good afternoon all Dear members of the SolarClub ))
I am planning to install Deye 8K-SG04LP3. In attachment - wiring scheme for Hybrid from Deye manual.

It show that L and N wire is branched. First line is connected to the "Inverter", the second line is connected to the "Home Load".
According to the manual "Max. AC Input/Output Apparent Power (VA)" - 8800.

That's my questions:

1)Do I understand correctly that if I turn on the "Home Load Device" with power 12 kWt invertor will not be damage?
Because of this schema invertor may will produce 8800w and rest power (12000-8800=3200w) will produce grid?
2) if someone has thay case in practice?

I would appreciate your help in answering!

P.S.
If I remember school physics correctly have parallel connection between Inverter, Home and grid. If resistance first branch lower than second one the most part current will be flow throw first branch
 

Attachments

  • deye_hybrid_wiring_schema.jpg
    deye_hybrid_wiring_schema.jpg
    175.1 KB · Views: 12
1)Do I understand correctly that if I turn on the "Home Load Device" with power 12 kWt invertor will not be damage?
Because of this schema invertor may will produce 8800w and rest power (12000-8800=3200w) will produce grid?
2) if someone has thay case in practice?
That is correct - it is standard configuration for a grid-tied inverter.

In practice this works because the inverter will increase the voltage at its grid connection, slightly higher than the incoming grid, so that it will power as much of the house load as possible. But if you draw more house load than the inverter can provide then the remaining power will come from the grid.

For safety reasons if the incoming grid gets disconnected, the inverter's grid port will stop generating power.
 
1) But if you draw more house load than the inverter can provide then the remaining power will come from the grid.
2) For safety reasons if the incoming grid gets disconnected, the inverter's grid port will stop generating power.

Thank you very SeaGal for answer!
I am sorry - not sure that quite understand you. That your message -" inverter can provide then the remaining power ... from the grid".
My concern is that invertor has limited ablity "provide the power". According to the instructions invertor can provide only 8800w. So you're saying about "can provide", but I concern if there is a extra demand - more than "invertor can provide"

My two questions are - If HomeLoad will demand ExtraMaxPower 3200w (12000-8800 = 3200 w ).
a) Invertor will not be damage?
b) If someone has this case in practice?

c) (for my own understanding question ). This ExtraMaxPower - will this extra power 3.2kWt flow into HomeLoad without "will or desire" of inverter? That is invertor will not managed this extraCurrent?

I want to apologize in advance.
English - is not my native )) May be I have "Lost in Translation ))" and I got it distorted.
 
Last edited:
Thank you very SeaGal for answer!
I am sorry - not sure that quite understand you. That your message -" inverter can provide then the remaining power ... from the grid".
My concern is that invertor has limited ablity "provide the power". According to the instructions invertor can provide only 8800w. So you're saying about "can provide", but I concern if there is a extra demand - more than "invertor can provide"
Extra power will come from the grid.

My two questions are - If HomeLoad will demand ExtraMaxPower 3200w (12000-8800 = 3200 w ).
a) Invertor will not be damage?
No damage - that is how they are designed to work, as detailed below.

b) If someone has this case in practice?
Yes, I do and so do millions of others with grid-tied inverters :)

c) (for my own understanding question ). This ExtraMaxPower - will this extra power 3.2kWt flow into HomeLoad without "will or desire" of inverter? That is invertor will not managed this extraCurrent?
Yes. When grid-tied, both the inverter and grid will supply power together, as needed by the house load.

The inverter synchronises its AC grid port output to match the frequency and phase of the incoming grid and will increase its voltage to allow current to flow from the inverter to the house load (and possibly out to export power to the grid, if not specifically restricted).

But, obviously, at some point, either because there isn't much sun or because you reached the limit of the inverter's power output, it can't power enough to keep the house load supplied. At that point, the remaining power will automatically come from the grid, so if the house load is 12000W and the inverter is providing 8800W, then the shortfall of 3200W will be imported from the grid.

Now, you're going to ask how does that work? ;) This is where ohm's law comes in; V=IR and P=VI. And remembering that the wires from your inverter to the house and from the grid to the house and from the house to the load all have a resistance, albeit (hopefully) very small.

Let me give you a very simplified example, ignoring the effects of inductive loads and grid voltage fluctuation...
- A load 12000W load is switched on and the voltage at that load is 240V.
- A load of 12000W will draw a current of exactly 50A at 240V.
- Let's say the voltage arriving at the house from the grid is 240.7V
- And assume that the resistance of the wire from inverter's grid port to the house load is 0.1 ohms.
- And assume that the resistance of the wire from house grid connection to the house load is 0.05 ohms.
- The inverter can only provide 8800W, which at 240V will be 36.7A.
- So to provide that power of 8800W, the inverter will increase its output voltage by 3.67V (from 36.7A x 0.1 ohms) at its output.
- Hence it is generating a voltage of 243.67V. This will cause 36.7A to flow from the inverter to the house load.
- The remaining current of 13.3A will come from the incoming grid voltage of 240.7V across the 0.05ohm resistance from grid to house load. (0.7V = 0.05 ohms x 13.3A)

In practice, the house loads and grid voltage will fluctuate, so the inverter will typically monitor the incoming voltage once a second and adjust its output voltage to deliver the necessary power. If the house load is less than the inverter's output, then the voltage increase from the inverter will result in current flowing from inverter to grid and you will be exporting power back to the grid (which will be consumed by your neighbours in a similar manner to that described above.)

The use of a current measuring CT clamp in a feedback loop to the inverter is used to either restrict export power if that is needed and to prevent any wasted battery power being exported to the grid when running off batteries.

Please note this is a very simplified explanation, but hopefully enough to get the general idea of how a grid-tied inverter behaves
 
Last edited:
Thank you very SeaGal again for explain..

It turns out that the whole point is the parallel connection of the inverter and the grid. And for the flow FromGrid-ToLoad exist, it is necessary that the grid-EMF be higher than the Inverter-EMF.. Right?
 