Max panels in series for eg418kpv PV input

Jdcarrol

New Member
Joined
Aug 5, 2023
Messages
47
Location
Phoenix
Hello, for the 3pv inputs which have a max of 600 voc, I’m having a hard time correctly finalizing if I can run 12 or 10 in a series, let me attach an image of our panel data sheet.

I understand for ambient temperatures down to 31 degreees I multiply voc by 1.10.

That electric guide was assuming the base rating was done at 25C. My data sheet looks like it’s providing numbers based on 20C, so do I not need to use such an aggressive multiplier? Difference is 10 vs 12 panels.

@FilterGuy
 

Attachments

  • IMG_5692.jpeg
    IMG_5692.jpeg
    117.7 KB · Views: 4
I understand for ambient temperatures down to 31 degreees I multiply voc by 1.10.
Just to be sure..... are you saying 31F is the lowest you ever will get? That is -.6C. that rounds to -1C.
My data sheet looks like it’s providing numbers based on 20C,
The 20C is from NMOT. You must use the STC value (25C).


The Beta for your panels is -.29%/degC. That works out to a multiplier of 1.075.

With a STC Voc of 49.7, the temp adjusted voc is 49.7 x 1.075 =53.18 12 panels would give you 638V
 