Modular system advice - dual SOK battery banks, SB175, Victron

mattleonard

New Member
Joined
Mar 8, 2020
Messages
76
Location
Oakland, CA
I'm building a semi-modular off-grid/ESS system in a 5' x 8' cargo trailer for special event (not daily) use, and looking for design feedback. I was interested in the EG4 6000xp - but won't have split-phase charging ability, and getting to the minimum 120v MPPT will be challenging with the small roof footprint. While I do plan to have 2nd fold-out array, having the ability to charge with just the ~600w array on the main roof is vital, and I'm not finding panel options to get the voltage that hight. So, leaning towards a Victron system - between reliability, surge capacity, and lower MPPT voltage minimum (~5v above battery - so ~57v) it seems like the best option.

I have (2) banks of (2) 48v SOK server batteries (each pair in a rack on wheels) for modularity, as ~200lb racks are still somewhat moveable. I may add a 3rd rack in the future, and having the ability to have discrete portable/rolling 10kWh racks (with the inverter rig on top) is a great form-factor. I was thinking the SmartShunt (vs Lynx Shunt), and I'll have a Cerbo for monitoring everything.

  • Any concerns using SB175 connectors? I have made these with 2/0 in the past (though parts are harder to source). I realize with the occasional disconnecting, I'll need to make sure to due the inverter pre-charge sequence each time.

  • Where to put the Class T fuse/s? Any issues mounting these directly on the battery terminals (like an MRBF terminal fuse)?

  • Switch - do I need it? The idea was if only using a single a battery bank I can ensure the unplugged SB175 isn't live. But the batteries all have onboard breakers, and I can use the SB175 insulator/boots to cover them when not in use.

  • Shunt - With closed-loop communication, do I even need a Shunt? If one bank is unplugged - will the Cerbo recognize the change in battery capacity, or will I need to re-program it?

  • Victron solar.png
 
Note that the +5V requirement is based on the Voc, not Vmp.

Vmp must stay 2V above battery voltage to continue.

Vmp should be at least 60V for a 48V LFP system.

  • Any concerns using SB175 connectors? I have made these with 2/0 in the past (though parts are harder to source). I realize with the occasional disconnecting, I'll need to make sure to due the inverter pre-charge sequence each time.

I personally hate them, but it's based on one bad experience. They seem to be fine in most cases.

  • Where to put the Class T fuse/s? Any issues mounting these directly on the battery terminals (like an MRBF terminal fuse)?

Where you have them looks good to me.

  • Switch - do I need it? The idea was if only using a single a battery bank I can ensure the unplugged SB175 isn't live. But the batteries all have onboard breakers, and I can use the SB175 insulator/boots to cover them when not in use.

Not really. You can shut off each battery individually.

  • Shunt - With closed-loop communication, do I even need a Shunt?

No.

  • If one bank is unplugged - will the Cerbo recognize the change in battery capacity, or will I need to re-program it?

I'm assuming you have a Cerbo in the system.

The master battery should send an aggregate value to the system. I do not know how effective it is at dynamic reconfiguration. I expect if you do a full shut down and restart when disconnecting/connecting batteries, the correct capacity will be communicated with the GX.

@HighTechLab will know for sure.

Recommend you one of the primary leads in each battery set to the other battery, i.e., (+) on one battery, (-) on the other battery.

1704692636931.png
 
The master battery should send an aggregate value to the system. I do not know how effective it is at dynamic reconfiguration. I expect if you do a full shut down and restart when disconnecting/connecting batteries, the correct capacity will be communicated with the GX.
We recommend a restart of the Cerbo just for good measure, but technically it can make the change live on the fly.

I have not seen a 1, 2, 1+2, off switch that is rated for 58v to date. Most of these rotary type switches are rated for up to 48v.
 