Mine are 1944 ah for a 48V system, with 9 batteries in parallel. It is more than 50% useable as these cells are vented flooded lead acid batteries, not valve regulated lead acids. Its pretty comparable to what a BMS would cut off a lithium bank off at. I thought it was around 50% too, until I talked to the engineers who load test and set the battery curves for these cells.
I don't care who or what they say. There is no magic to these things. Properly maintained FLA has a much greater potential for extended life, but the issue is many don't properly maintain them, and AGM end up lasting longer.
Anyways, I don't care what my total % usage is as I will never remotely get close to using anywhere near its capacity. I was just wondering, when they advertise/stamp on the side of these lithium powerwalls (not necessarily tesla) if they are taking the high end voltage for their calculation. In my case, I have to do the math for these guys. They originally used 1.75 volts for their calculation because I gave them a discharge curve that was based off a 1.75 volt starting point. I was able to get them to use 2V volts for their starting point, but was curious if 2.25 volts was doable or not. The engineer I talked to said the cells would stay at 2.1 volts after I lost the grid for hours. But It sounds like battery banks are determined by nominal voltage. I appreciate your input. thanks.
The only reason I can think that someone would use 1.75V for nominal lead acid is to de-rate them... and allow you to use > 50% and still seem like you're getting something.
1944Ah * 48V = 93.3kWh, 46.7kWh usable
With lead acid, your capacity is calculated based on 2V/cell. Period. ALL batteries are rated via nominal voltage.
One inconsistency with lead acid is the rate rating. MOST batteries rate Ah at the C20 value, i.e., 20 hours at continuous 5A discharge can deliver 100Ah. Use more current, you get less Ah. Use less current, you get more Ah. In the EU, "solar" batteries are rated at their C100 value, i.e., whatever current they can deliver for 100 hours yields X Ah. In higher load applications like forklifts or for high power, short duration backup, they may use the C10 rate, i.e., the current they can deliver for 10 hours. This Ah rating is lower than C20 rating. Many quality batteries intended for this application list MULTIPLE ratings to help the customer determine what is best for their application.
FWIW, Nominal Voltage exists for this purpose. This is also, roughly, the "average" voltage experienced by the battery throughout the entire discharge to empty. If you actually measure Wh live, and calculate out the voltage, it always comes out really close to the defined nominal.
Put another way, if someone used the peak charge voltage to define battery kWh, and you measured the kWh extracted during a discharge, you would NEVER achieve the quoted value.