Question on SolArk 15k SolarEdge AC system with batteries

MikeSpeegle

New Member
Joined
Sep 13, 2023
Messages
59
Location
Crowley, Texas
I just found out I need to use both sets of terminals. I have 4/0 welding wire from Victron and 2/0 for each 51.2v 250ah series string and 1/0 between batteries in string. I have 250 amp fuses in the Victron for each parallel string and a 500 amp fuse which will only trigger in with a problem as 15k would never use more than 275 amps.

Now they say I need two sets of wires 4/0 to each pole in SolArk. Can I use a 500amp 3 pole busbar after the switch and shunt to send two wires. Will my short runs to fuse and switch be ok?

Or should I use Y adapters from home grid on my already ran 4/0 cable?

Not trying to pin someone with an answer just asking for suggestions that I will take full responsibility using.

Last question are the two black rings for the battery cables necessary because I forgot them.

Thanks!!!!



IMG_0750.jpegIMG_0881.jpegIMG_0880.jpegIMG_0879.jpeg
 
Bussbar from battery to inverter is fine. That is how mine is setup. You can have it inside the trough. Put the battery connection between the two sol-ark connections. Put on the doughnuts near the sol-ark when you rewire.
 
I think the manual specs 2/0 for using both inputs. I have 4/0 from my battery to the buss bars and then dual 2/0 from bus bars to SolArk.
 
I did 4/0 to fuse then switch then busbar and the a very tight two pairs of 4/0 to SolArk see attached. All wires from busbar to SolArk are same size positive and negative. The positive and negative before are close.
 