Renogy 3000W incorrect wire size on installation manual?

ee.va

New Member
Joined
May 24, 2023
Messages
1
Location
Vancouver
Hi All,

I've been skimming through the Renogy 3000w inverter charge manual and it states the following:

1683051068760.png

I followed up by checking with the NEC Amperage Tables. 4/0 is well below the threshold of 300A only rated at 230A at 75 degrees C.

1683050524949.png

Even the 12V 200Ah battery from Renogy rated 4/0 cable for 230A.


2023-05-24 15_59_38-RBT200LFP12-BT-G1_manual_V1.0.pdf — Mozilla Firefox.png

My gut feeling is off on this one, would appreciate any expertise regarding this situation.
 
There are higher grade ratings, 90°C can handle 260 and 105°C (marine grade) can handle more - 200°C silicone wire even more.

According to this website, their 4/0 can go 445 (near the bottom of the page):


I personally push ~300A through 2/0 marine grade @12V for 15 minutes at a time. The wires get warm, but they are not hot.
 
Another thing that changes the ampacity ratings of wires is if they are running alone in free air or are in a conduit with other wires. The ratings in your tables match NEC tables for up to 3 wires in a conduit which gives 175A and 230A for 2/0 and 4/0 copper respectively with 75 degC rated insulation.
Sub-table 310.15(B)(2)(a) lists further ampacity reduction if more conductors are in the conduit, like 50% rating for 10-20 conductors.

The table 310.15(B)(17) for free air lists those same wires at 265A and 360A because the free air around the wire will allow better heat dissipation. Wiring from a battery to the inverter is commonly done in free air and so the Renogy table would be OK.
 