why do you need a shut off between SCC and BUSS BAR (not battery)? If you shut off inbound solar energy, there's not reason for a separate shut offIs it safe to put a shut off switch between the solar charge controller and the battery?
I think I remember hearing that could damage the charger if it’s hooked up to panels with no output, but wanted to double check.
On solar my advise (espically if not tilting), is to put as much as you can on the roof.
why do you need a shut off between SCC and BUSS BAR (not battery)? If you shut off inbound solar energy, there's not reason for a separate shut off
Right, but usually it's from the panels to the SCC, not the SCC to the battery. There's no reason you can't and it would provide protection between the SCC output and the battery, but not necessarily needed.For some, covering panels may not be an easy thing to do. MC4 connectors are not to be disconnected under a load. A dual pole breaker is an easy and safe way to cut off PV power into the solar charge controller.
Correct, at least according to the Amazon posting they're AC only.I hate to say this, but I think those are AC breakers. You need DC breakers. The Chtaixi DZ47N-63 breaker has an AC rating and no DC rating.
If you are going full-time in that rig, ( and don’t think you will change rigs), I would make a frame of aluminum and have the roof completely covered. That way you have panels over the vents and A/C’s. This will keep the sun off the roof (cooler and no sun damage) and you can use larger (cheaper per watt) panels.