Hi all. New here. I've one of the DC Solar trailers.
I've connected the output (AC1) to an isolated subpanel in an outbuilding. Works fine...until there isn't enough sun long enough.
I connected grid power to AC2 hoping the system would pull from the grid when the batteries and PV system won't supply enough power, but use the batteries first.
When I do this, after a short delay, the Grid icon shows up on the Sunny Island display, but then the Sunny Island starts pushing power into the grid. A few moments later the Sunny Island disconnects from the grid with warning W501, Grid Reverse Current Prevented.
On the Ext General menu, 231.05 I've tried both Gen and GenGrid.
I have 232.08 set to GridCharge.
Does anyone have any suggestions on what I have to do to keep this thing from sending any power back into the grid?
Thank you.