No idea about the Sofar, but my Solis has a menu option to cut off export power limitation if the RS485 connection to the grid CT/Acrel power meter fails. On the Solis, it is enabled by default.
So first question is have you set export power limitation - this presumably will need to be on in the first place for the inverter to have something to cut off?
Secondly, is there a menu option to cut off when export power monitoring fails?
Presumably to test the installation is working in anticipation of a potential DNO inspection prior to commissioning?i thought that if it is on the ENT listing as approved, which it is, then its approved already, so not sure why you would be having to test it?
what size battery bank are you using? is that the reason youre testing for G100?
Not according to the DNO.Ah! just looked it up.
Assuming it is this one..
Then it is only 3kW inverter so comes under G98 compliance and not G99/G100. So there's no G100 to check
That's odd, if the inverter is G100 compliant, it would have export power limitation settings.
I'm not familiar with that device, but what is its output power?
For < 16A per phase (3680W) it should be G98 compliant.
For > 3680W, it should be G99 compliant with optional G100 compliance.
Do you have a link to the specification of your specific model?
I suspect that we don't have all the information.i too am confused.
You are absolutely spot onI suspect that we don't have all the information.
My wild guess (and I hate making guesses) is that he already has a grid-tied PV inverter and is looking to add this energy storage inverter. So, although the Sofar ME3000SP is G98 compliant and only needs 'notification-after-install', because he already has an inverter this is pushing him into G99 territory and his DNO has specified that a maximum export is adhered to, hence the need for G100 export power limitation. But, as I just a pure guess.
that makes sense now, are you happy to share the details/content/cost of your application please, i think i may have to do the same. i have actually removed my Sofar (which was installed for two days) as i wanted and acquired a bigger inverter (Sunysnk 5kw) to take advantage of a higher charging rate from the grid overnight, and didnt want to make more than one application. as the electrician i am using is not MiCS he doesnt have experience or knowledge of the paperwork/application side, so i am doing that part.You are absolutely spot on
Been back & forth to Sofar tech support but still no definitive answer. Still waiting for confirmationIn which case the Sofar won't normally be exporting any energy (hopefully), so all you will need is for it to have the ability to shut down if it looses grid import/export measurement, which is what you were presumably asking about in the first post.
Have you tried Sofar tech support / customer care / whatever they call it?
What size is your battery bank? I have removed my Sofar after a day or so as I really wanted a bigger inverter to be able to charge my intended 28.6kw battery system.I initially applied for the permission of the installation of the battery storage using the fast track application. I already had the full allowance for export from my PV @ 3.6kW under g98.
I received a reply from northern power grid allowing the installation under the fast track but had to complete the g99 form A3.2 & g100 commissioning form.
The maximum intrinsic design capacity of all generation equipment is no greater than 32A.
If you want to go over the 32A then it's a full g99 application.
The application falls under SGI-3, which I have questioned but currently have not received a reply.
Keep us updated - may look into a 2nd inverter in the next year or so.I will have a look at what I need to do and start the application when I return to the UK from holiday
IIRC, the DNO reserve the option to be present during commissioning - so that they can observe the various tests (such as inverter shutting down if grid monitoring comms is lost) perform correctly.Or am I missing something major.
I got various emails - one of which was receipt of application, then a bit later one that explicity stated the application was approved.Today I received a reply that the forms have been received & logged in their system.
So I assume all is OK.
Is that your G99 application. I have one in at the moment since begining of July and heard nothing. Wondering if I should go ahead and install and send in the commissioning sheets A3-2 and G100.I got various emails - one of which was receipt of application, then a bit later one that explicity stated the application was approved.