I'm enclosing a screen room and will add a mini-split for cooling (in AZ). Since we lose power a lot here I thought it might be worth it to buy one of the solar powered units either from EG4 or Airspool. The Airspool unit is now Energy Star rated so I figured that's the way to go.
Then the details snuck up on me.....
The questions / obstacles I have run into are:
Issue #1: These units require at least 80VDC to operate, and the 4-panel 'kit' offered by some resellers puts you in the 200 - 250VDC range (panels in series). That voltage then requires DC Arc Fault protection - and I've yet to find a UL listed AFCI rated for DC. Even the non-UL breakers that meet the spec are well over $400 on Amazon...
Issue #2: Since it's high voltage, the neutral current carrying connector (B-) must be bonded to the equipment grounding connector. If this does not happen within the heat pump itself (similar to the way inverters handle this) then I must proving a bonding lead somewhere. Within the roof top junction box perhaps? So I assume I can just connect the B- box in & box out leads to the EGC terminal block or must I use a wire nut?
Related to Issue #2: IF the heat pump DOES bond the B- to EGC internally, then that means that the suggested way to connect it to AC using a standard 120v 3-prong plug (for 12KBtu and smaller units) will NOT meet code. Unplugging the unit would break the B- to EGC bond. So I still need a hard wired service disconnect. (Awaiting a tech reply from Airspool - who has been very responsive BTW).
Issue #3: Since the high voltage DC must use a bonded B- conductor, the NEC requires that wire color to be either Grey or White. The cable sets offered in the kits are all red & black. So no using pre-made cables with MC4 connectors - I'll have to make my own. Crimpers, connectors, etc are now added to the list.....
Issue #4: Since it's high voltage DC, I cannot run the EGC inside the same conduit as the B+ / B- conductors? What about putting the EGC inside the same roof top junction box? Doesn't make too much sense to me.... two conduits exiting the same junction box?
Issue #5: I do NOT plan to run the DC leads inside the house. Rather, I plan to penetrate the roof at the overhang and just run the conduit down the exterior wall to the heat pump. So can I use PVC conduit or must it still be EMT? In this heat I'll probably wrestle with the EMT though....
Issue #6: Finding UL listed PV disconnects, ground-fault breakers and enclosures that won't break the bank....
These solar-powered mini-splits may not be quite as plug-n-play as the marketing folks would have me believe.....
Then the details snuck up on me.....
The questions / obstacles I have run into are:
Issue #1: These units require at least 80VDC to operate, and the 4-panel 'kit' offered by some resellers puts you in the 200 - 250VDC range (panels in series). That voltage then requires DC Arc Fault protection - and I've yet to find a UL listed AFCI rated for DC. Even the non-UL breakers that meet the spec are well over $400 on Amazon...
Issue #2: Since it's high voltage, the neutral current carrying connector (B-) must be bonded to the equipment grounding connector. If this does not happen within the heat pump itself (similar to the way inverters handle this) then I must proving a bonding lead somewhere. Within the roof top junction box perhaps? So I assume I can just connect the B- box in & box out leads to the EGC terminal block or must I use a wire nut?
Related to Issue #2: IF the heat pump DOES bond the B- to EGC internally, then that means that the suggested way to connect it to AC using a standard 120v 3-prong plug (for 12KBtu and smaller units) will NOT meet code. Unplugging the unit would break the B- to EGC bond. So I still need a hard wired service disconnect. (Awaiting a tech reply from Airspool - who has been very responsive BTW).
Issue #3: Since the high voltage DC must use a bonded B- conductor, the NEC requires that wire color to be either Grey or White. The cable sets offered in the kits are all red & black. So no using pre-made cables with MC4 connectors - I'll have to make my own. Crimpers, connectors, etc are now added to the list.....
Issue #4: Since it's high voltage DC, I cannot run the EGC inside the same conduit as the B+ / B- conductors? What about putting the EGC inside the same roof top junction box? Doesn't make too much sense to me.... two conduits exiting the same junction box?
Issue #5: I do NOT plan to run the DC leads inside the house. Rather, I plan to penetrate the roof at the overhang and just run the conduit down the exterior wall to the heat pump. So can I use PVC conduit or must it still be EMT? In this heat I'll probably wrestle with the EMT though....
Issue #6: Finding UL listed PV disconnects, ground-fault breakers and enclosures that won't break the bank....
These solar-powered mini-splits may not be quite as plug-n-play as the marketing folks would have me believe.....