Just got done installing a mini-split and removing it shipping it back to the seller, but I did install wire and disconnect box. I accidently bought a fused disconnect what I did was put 25amp fast blow fuses which is what the sticker on the mini split stated max fuse size was 25 amps for the 9000 BTU. I pulled 10AWG to my panel and put a 30 amp breaker. I already had a few double pole 30 amps I just removed the bridge between the double pole and made the breaker into 2 single poles. Saved some money there.
This is what I would get make sure you put in a disconnect right next to the outdoor unit.
30 amps non-fused
disconnect from Home Depot is $20. It's 120 or 240 I just wire up the hot and neutral to the disconnect I was using 120V if 240V then pull a black, red, and a green for ground. Black and Red will go through the disconnect grounds go to the ground bar in the middle. Use 1/2" liquid tight metallic flex
conduit as a whip from the disconnect to the outdoor unit. I prefer the metallic liquid flex conduit just lasts lot longer like having the metal passing an extra ground back to the my main just incase that way if a case got energized somehow it would not be isolated from the ground of my box using non metallic flex would do that.
Run 1/2" EMT conduit to your panel to the disconnect. Run THHN stranded 10AWG wire from the panel to the disconnect then on to the mini-split inside the flex conduit. Put a whatever breaker the AC unit calls for that way it will protect your compressor just can't go higher then 30 amps for 10AWG.