My system currently lacks any means for the Orion BMS to communicate a shutdown request to the Schneider XW+. The Orion can call for 2.2kW grid input when it reaches a set low SOC, but it's possible our load could inadvertently outpace the 2.2kW and keep draining the battery bank.
Long term I have two possible solutions:
- Double the 2.2kW to 4.4kW so that load outpacing the backstop input is ruled out.
- Enable canbus comms between the Orion and the Schneider so that it can communicate a shutdown request.
In the meantime my low battery failure modes are:
1. Inverter observes LBCO by the voltage at it's terminals and shuts itself down (preferable)
2. Orion observes sustained cell <2.5v or pack <40v and opens it's contactors under load (not preferable)
What LBCO voltage would be most likely to achieve result #1 before #2, but with the least likelihood of an early "false alarm" LBCO event?
46v, 44v, 42v, 41v?